I want to install a DPST switch between a disconnect box and a well pump. I installed the switch and when the switch is in the"ON" position, the pump works fine. When I turn the switch to the "OFF" position, the relay in the disconnect box chatters (very rapid on-off) until I dosconnect the power. Any ideas sas to why the chatter?
 

·
Banned
Joined
·
17,158 Posts
Post a schematic of how the switch is wired from the panel to the switch, to the relay, to the pump. If it is chattering, that means it is still getting voltage through current leak. What is the rating on the switch & relay?
 

·
Registered
Joined
·
9,284 Posts
Probably has something to do with the way the pressure switch is wired or whether its connections were disturbed when you installed the new double pole switch. I cannot speculate on it without seeing how the pressure switch and the relay are wired. Posting a picture of the wiring diagram (if there is one and it is still correct) can help.
 

·
Idiot Emeritus
Joined
·
1,910 Posts
With most pumps, there cannot be any switch between the control box and the pump motor. If these lines are switched off, the start relay and that start capacitor will form an inductive-reactive circuit. Basically, they'll fight with each other. This is the chatter you're hearing.

The switch can be installed anywhere in the line from the panel to the control box, and it'll work fine.

Rob
 

·
Registered
Joined
·
4,728 Posts
We have a similar situation with a waterfall pump at my work. When it is powered down, the relay chatters. In our situation it is the pump running backwards when it is shut off as the water "backflushes". When the water is gone, the chatter stops. By design we do not use a check valve as this "backflushing" clears any debris around the pump.
 

·
Registered
Joined
·
2 Posts
Discussion Starter #7
With most pumps, there cannot be any switch between the control box and the pump motor. If these lines are switched off, the start relay and that start capacitor will form an inductive-reactive circuit. Basically, they'll fight with each other. This is the chatter you're hearing.

The switch can be installed anywhere in the line from the panel to the control box, and it'll work fine.

Rob
Rob, your answer fixed my problem. Thanks for the quick response - Rich
 