I got the chart but what to understand the following:yuri said:What chart? Click on Go Advanced and follow instructions to upload a jpeg etc.
Thanks for the reply. I understand that, but not sure if the pressure values listed on the pressure temperature chart are suction pressure values or discharge pressure.JJboy said:The temperature is related to the pressure. When the temperature changes the pressure increase or decrease.
R22 shows 34 F at 60psi and 93F at 180psi. At 70F the pressur is showing around 120psi.Marty S. said:So long as there's a saturated mix of both liquid and gas present it covers everything. Look at your chart and tell me what the R22 temp shows with a suction pressure of 60. Now look at the chart and tell me what it is on a 180 psig liquid line. How about a R22 tank with vapor and liquid in it at a room temp of 70 degrees?
I will wait for your response.Marty S. said:So long as there's a saturated mix of both liquid and gas present it covers everything. Look at your chart and tell me what the R22 temp shows with a suction pressure of 60. Now look at the chart and tell me what it is on a 180 psig liquid line. How about a R22 tank with vapor and liquid in it at a room temp of 70 degrees?
I mean when to compare the pressure values on the PT chart with the actual suction pressure reading on the ac and when to compare with the actual discharge pressure readingJJboy said:1)The pressure values listed on this chart are suction pressure or discharge pressure?
Compressor does the change low pressure to high pressure. So the temp changes low to high temp..... What is your question?
I mean when to compare the pressure values on the PT chart with the actual suction pressure reading on the air conditioner and when to compare with the actual discharge pressure readingMarty S. said:That's all there is to it,a relationship between pressure and temp for a given refrigerant. You have a system running 60/180. The suction line measures 50 degrees so how much is the refrigerant super heated ? The liquid line measures 80 which means you have what for subcool?
Does the temperatures on the PT chart indicate the ambient temperature or the pipe temperature?JJboy said:The difference between the temps that you are measuring with a thermometer and the values of PT chart are due to the SH and SC
I think technicians check the suction pressure on the system and compare it with the pressure on the PT chart to see if their actual reading on the system is off and they do the same thing with the discharge pressure. Am I right sir?JJboy said:PT chart indicate the temp of the environment where is the refrigerant. The pipe temperature it's the measured temp
Thanks beenthere for the detailed explanation. One question: when does the ambient temperature used on the PT chart? I mean for an ac system in a room.beenthere said:The pressure and temps on the PT charts are saturation pressures and temps. They are not suction or discharge temps or pressure. this is the pressure the refrigerant will exert at X degrees provided that both liquid and vapor are in the container(as said earlier).
The chart is used to determine the amount of subcool or superheat the system is operating at. Not what it should be operating at.
Take a new cylinder of R22, at 32°F it will have 58PSIG in it. At 83°F the same tank with the same amount of refrigerant in it will have a PSIG of 180. The reason is that it is a saturated refrigerant. Meaning that the refrigerant is existing in the cylinder as both liquid and vapor. As the refrigerant warmed up, more of the liquid boiled off to vapor, and the vapor takes up more space then the liquid did, so the pressure increased. But the total mass in the cylinder remained the same.
You may want to read up on "saturation".
Ambient temperature has nothing to do with a PT chart. It has to do with the refrigeration pressure and temperature.Samart said:Thanks beenthere for the detailed explanation. One question: when does the ambient temperature used on the PT chart? I mean for an ac system in a room.