I have a crown boiler that is about 16 years old. Just recently the pressure relief valve started leaking. I replaced bothe the pressure relief valve and the expansion tank and the pressure still bulds up over the 30psi. Any suggestions?
I came across this once - very frustrating. I eventually found out that the bottom port of the spirovent/air scoop where the expansion tank gets screwed-in was clogged with sediment - basically forming a dam such that the expansion tank was rendered useless. I think someone must've used copious amounts of boiler seal liquid to "fix" a leak somewhere in the system.I have tried just about everything I can think of and also what's been suggested and the pressure relief valve continues to leak. I have bled the pressure down to 20 psi and as long as the boiler doesn't run it stays constant. As soon as the boiler starts up the pressure begins to increase until it reaches 30 psi and then it drips. Once the boiler shuts off it will drop to about 28 psi and remain constant.
Any more ideas?