Having what appears to be an issue with the heat, the issue being not enough. house has hot water BB heating with a boiler made/installed during the Nixon administration, and I have no idea what it's make/model is.

House isn't heating up normally, it IS heating though. Stat was set to 72* but the temp was only getting to 68* and staying there. I thought it was just a case of being so cold out ( combined with the terrible 1960's insulation ), that the system just couldn't keep up. Dialed back the stat to 68* and the temps dropped to 66* and stayed there.

Boiler is firing, and the pump motor is running, that I visually verified. The circulation pump is a huge contraption - fairly large impeller housing with a motor the size of one on a table saw attached to it. That's compared to the circ pump on my old house which was smaller than the impeller housing on the one I'm in now, "all-in", motor and all.

I can feel water going through the pipes.......but the baseboard units just aren't putting out much heat??? Is it possible the impeller broke, or stripped off the shaft enough that it still spins, but just not at the velocity/volume it's supposed to?
 

· Master General ReEngineer
Joined
·
10,531 Posts
The circulation pump is a huge contraption - fairly large impeller housing with a motor the size of one on a table saw attached to it. That's compared to the circ pump on my old house which was smaller than the impeller housing on the one I'm in now, "all-in", motor and all.
Ayuh,... The biggest difference in the pumps is time, 'n technology,...

My guess is the Big 1 is original, 'n Yes, they do wear out...

Ya oughta be able to swap in a New style pump with little to no extra effort...
 

· Registered
Joined
·
1,796 Posts
Impellers wear out/ water pressure can be too low/ baseboard fins get dust filled so less house air goes through them/ the operating limit needs recalibation/ air in the baseboards/ incorrect anticipation set up in thermostat.

The impeller can wear out but the clutch between the motor and the impeller either works or it doesn't.

PS That pump & motor of yours probably has 3 oil spots in serious need of non detergent oil.
 

· Registered
Joined
·
39 Posts
Is it a big red one, and old Bell and Gossett?

If it is, you should be able to replace with a Taco 007. Standard pump sold in Lowes and HD. There are a number of other possibilities. Check the system pressure, with boiler up to temp it should be above 12psi but less than 30psi. What is the temperature of the boiler? Could the system be air bound?
 