when I touch it without shoes on standing on a bluestone step. Porch is concrete with the railings mounted into the concrete. I didn't believe it until the wife showed me. Anyone have any ideas on how to fix this? Or the cause? Thanks
 

· IBEW electrician
Joined
·
14 Posts
I would call an electrician, a good one, and have him get over and check it out for you. It's not something you should be doing yourself it can be pretty dangerous. Out of curiousity have you had any other elctrical issues recently?
 

· Registered
Joined
·
37,499 Posts
Post a picture of these railing so we can see what your seeing.
Are they attached to the wall?
If so someone may have ran the screw into a wire.
 

· Semi-Pro Electro-Geek
Joined
·
3,404 Posts
Just get an electrician out there to handle it ASAP. That's a very dangerous condition. What feels like a small tingle one time may cause a fatal shock the next time you touch it. Some things are good DIY projects to learn troubleshooting skills on. This is not one of those situations. Hire a pro today.
 
  • Like
Reactions: Gymschu

· Registered
Joined
·
8 Posts
Discussion Starter · #9 ·
1st pic is from the front of house; 2nd from the back. From the front, got a small shock on the rails that go down along both sides of the steps and not on top porch along the long rail. From the back, got shock from the right side step rail only and not the left. Where there are screws into the wall (3) is on front right side rail. I backed them out and still a shock. Last nite, no shock at all on any rails. Will check today.
 

· Registered
Joined
·
14,953 Posts
Very nice looking porch, or should I just call it hot :).
Is that Aluminum siding?

You need to get a meter from the problem railing to earth ground which would then show the voltage you are (I assume) feeling. Then turn off breakers until you find the one powering the problem.

Here is the concern you (sorry to be blunt) are ignoring. That railing could be connected directly to 120 volts. You may only feel a tingle because you are not at that moment completing a good ground path, but let it rain a bit to provide better contact and someone could get hurt. We have no idea as to your capabilities but here it is Saturday and no mention of you having called an electrician.

If the siding is metal with the railing attached to it, the source of the problem could be anywhere.

Make us feel better, explain how you are qualified or tell us when the electrician is showing up.

Bud
 
  • Like
Reactions: mpoulton

· Registered
Joined
·
14,953 Posts
Vinyl is good,
Do you have a volt meter? A simple analog meter would be better than a digital. They are less than $20 and good to have around.

"Last nite, no shock at all on any rails." Were there lights that were turned off?

Somehow we need to get you to stop using yourself as a volt meter :(.

In a way, you don't want the problem to just go away before you find a cause as you will then never know when it might come back. Sure would hate to have a child be the victim.

Getting a reading on a meter and turning off breakers until it goes away would at least narrow it down to one circuit.

Bud
 

· Banned
Joined
·
17,162 Posts
Someone hit a wire with the screw. There is no way of measuring voltage when you have siding, because you are looking for ground fault.

Turn off breakers one by one, until there is no more current flowing.

The common practice for looking for a fault is to run a single piece of wire to a ground on one of the outlets outside, attach to the black meter lead. The Red you will check the railing, until the culprit breaker is found.

Make sure you are using a good meter, not some cheap one that will give you false readings.
 

· Registered
Joined
·
1,051 Posts
when I touch it without shoes on standing on a bluestone step. Porch is concrete with the railings mounted into the concrete. I didn't believe it until the wife showed me. Anyone have any ideas on how to fix this? Or the cause? Thanks
Where is your electrical service and meter in relation to the railing? Is it an overhead service or underground?

Were there any electrical lines buried in the ground before the porch was built?

Have the lights in the house been flickering?
 

· Registered
Joined
·
2,881 Posts
Where is your electrical service and meter in relation to the railing? Is it an overhead service or underground?

Were there any electrical lines buried in the ground before the porch was built?

Have the lights in the house been flickering?
I'm not an electrician but I have a good understanding of how it works, I've done HVAC work for the last 40 years or so and have seen a lot. This issue reminds me of a customer that was having issues in their place of business. I remember the secretary actually got shocked when she touched the commode handle. I don't remember but suspect they had light flickering issues as well. Turns out they had a problem with the neutral wire coming into the building. Seems the electricity was searching for a ground. I would be really worried about getting this fixed quickly. I think it's much more dangerous than the original poster realizes
 

· Registered
Joined
·
8 Posts
Discussion Starter · #16 ·
I found outlets with reverse polarity - 1 on the porch, 1 in the nearby bathroom, and 3 in a basement bar. They have been corrected. And so far no shocks on the railing. Do you think this could have been the cause? Thanks
 

· Semi-Pro Electro-Geek
Joined
·
3,404 Posts
I found outlets with reverse polarity - 1 on the porch, 1 in the nearby bathroom, and 3 in a basement bar. They have been corrected. And so far no shocks on the railing. Do you think this could have been the cause? Thanks
Only if there are other problems that are much more significant. How did you fix the receptacles? Were the wires mislabeled, or just connected to the wrong terminals? Was it only H-N reversed, or was ground involved?
 

· Registered
Joined
·
775 Posts
I'll expand on mp's post. Was a jumper between the ground terminal and neutral terminal with reverse polarity? A reverse polarity bootleg ground is very dangerous and difficult to detect. It's the only time a non contact tester trumps a voltmeter.
 

· Registered
Joined
·
5,468 Posts
I'll expand on mp's post. Was a jumper between the ground terminal and neutral terminal with reverse polarity? A reverse polarity bootleg ground is very dangerous and difficult to detect. It's the only time a non contact tester trumps a voltmeter.

A bootleg neutral some where as well as reverse polarity could
explain the whole scenario !
 