Labeling the breakers and putting in the double pole breakers is straightforward, but it's a shame home inspectors are this bad nowadays. I thought 8 conductors in a conduit would need derating or pose a code problem. Is that not correct?I wished my panel looked half that good. Minor issues, easily corrected.
Handle ties only became code in 2008.
Multiple circuits in a conduit is fine.
Only 8, but that's good to know. I thought it kicked in at less than that.Most HIs don't remove panel covers. Yes derating is required for more than 9 #10,12, or 14 conductors. Are there more than 9 in a conduit? Derating may be accounted for.
I guess for the same reason that code requires them to be handle tied now. When working on a MWBC circuit it would be important to kill both circuits when say removing the shared neutral on a receptacle.Why do you expect a MWBC to labeled ?
There is an underlying assumption that people removing the dead front on a panel know what they are doing.
If it is wired correctly there will not be a shared neutral on a receptacle. The neutral is pigtailed to the receptacle?I guess for the same reason that code requires them to be handle tied now. When working on a MWBC circuit it would be important to kill both circuits when say removing the shared neutral on a receptacle.
I actually meant to write circuit, but instead listed receptacle. You are correct though.If it is wired correctly there will not be a shared neutral on a receptacle. The neutral is pigtailed to the receptacle?
By opposing buses, you mean a bus for each phase of the split-phase, and only one of the buses is feeding the MWBC? That should be changed immediately--it means the current on the neutral can be double what is permitted by code.I've already found one MWBC that isn't on opposing buses... I'm not sure what code cycle they were on back then. When did MWBC's start needing to be handle tied in code? In this case I will obviously help him upgrade to double pole breakers
That's correct, and it was the first thing I addressed for him. There's a finished basement and circuits were obviously added for that after the home was built. I'm guessing during that process the two breakers of the MWBC were inadvertently placed on the same bus.By opposing buses, you mean a bus for each phase of the split-phase, and only one of the buses is feeding the MWBC? That should be changed immediately--it means the current on the neutral can be double what is permitted by code.
I think this is your best option.I can remove furnace neutral at that point and run an individual neutral back to panel to put furnace on its own circuit (it is a long run back to the panel from that point however.)