Pool timer

1662 Views 3 Replies 3 Participants Last post by  pete1950
I have a t-104 Intermatic timer. It has A 1234 connection terminals with the load on the 2 & 4 terminals. The line are 1& 3 with 2 white wires from factory under the hubs. One thing which I am confused by is the old installation had a short white wire going from the A terminal to the grounding bar in the box. I put this back in the same way connected the load from the breaker on the 2 & 4 terminals and line on the 1-3 terminals on the timer with the white wires from timer. Turned back on power and motor works fine but timer does not run. Any ideas???
1 - 1 of 4 Posts


A terminal is not used, unless it is a 277 volt application, which you do not have .
Make ssure that line from breaker is on term 1 & 3, than load to term 2& 4.
See less See more