I've noticed over the years that homes and apartment built prior to the 70's often have a hot and cold shutoff in the wall somewhere, protruding like shower valves, usually near the toilet - for all water to the bathroom- tub/shower, sink. toilet. Since then these valves have disappeared as individual shutoffs would be incorporated under the sink and toilet - but not for a tub or shower. I figure changing valve washers was a pretty common thing that needed to be done regularly due to rubber washers...
But nowadays with washer-less ceramic cartridges, and the longevity of newer washer material (neoprene?) are under-sink shutoffs even really necessary? Or is there a code that requires a shutoff for a sink, but not a tub or shower, in bathrooms and kitchens?
 

·
Registered
Joined
·
37,222 Posts
If it's not code to have valves at every fixture, it should be.
I even install them on the tub and or shower.
Momma will not be happy with the water shut off to the whole house while your trying to do a simple repair.
 

·
Registered
Joined
·
5,858 Posts
Code requirement under IPC

INSTALLATION OF THE BUILDING WATER DISTRIBUTION SYSTEM
606.1 Location of full-open valves. Full-open valves shall be installed in the following locations:
1. On the building water service pipe from the public water supply near the curb.
2. On the water distribution supply pipe at the entrance into the structure.
3. On the discharge side of every water meter.
4. On the base of every water riser.
5. On the top of every water down-feed pipe in occupancies other than one-, two- and three-family residential occupancies.
6. On the entrance to every water supply pipe to a dwelling unit, except where supplying a single fixture equipped with individual stops.
7. On the water supply pipe to a gravity or pressurized water tank.
8. On the water supply pipe to every water heater.


606.2 Location of shutoff valves. Shutoff valves shall be installed in the following locations:
1. On the fixture supply to each plumbing fixture other than in individual sleeping units that are provided with unit shutoff valves in hotels, motels, boarding houses and similar occupancies.
2. On the water supply pipe to each sillcock.
3. On the water supply pipe to each appliance or mechanical equipment.


606.3 Access to valves. Access shall be provided to all full-open valves and shutoff valves.
606.4 Valve identification. Service and hose bibb valves shall be identified. All other valves installed in locations that are not adjacent to the fixture or appliance shall be identified, indicating the fixture or appliance served.

Full open valves are Ball or Gate type.
Shutoff valves are compression and any type.
 

·
Registered
Joined
·
2,060 Posts
Today you can get rough in shower faucets with hot/cold screw shut offs, accessible when you remove the cover plate.
Shut off valves are a must.
Shut off valves that function are even better.
I replace shut off valves and angle stops that are hard to turn on a regular basis.
 

·
Registered
Joined
·
3,022 Posts
Code requirement under IPC

INSTALLATION OF THE BUILDING WATER DISTRIBUTION SYSTEM
606.1 Location of full-open valves. Full-open valves shall be installed in the following locations:
1. On the building water service pipe from the public water supply near the curb.
2. On the water distribution supply pipe at the entrance into the structure.
3. On the discharge side of every water meter.
4. On the base of every water riser.
5. On the top of every water down-feed pipe in occupancies other than one-, two- and three-family residential occupancies.
6. On the entrance to every water supply pipe to a dwelling unit, except where supplying a single fixture equipped with individual stops.
7. On the water supply pipe to a gravity or pressurized water tank.
8. On the water supply pipe to every water heater.


606.2 Location of shutoff valves. Shutoff valves shall be installed in the following locations:
1. On the fixture supply to each plumbing fixture other than in individual sleeping units that are provided with unit shutoff valves in hotels, motels, boarding houses and similar occupancies.
2. On the water supply pipe to each sillcock.
3. On the water supply pipe to each appliance or mechanical equipment.


606.3 Access to valves. Access shall be provided to all full-open valves and shutoff valves.
606.4 Valve identification. Service and hose bibb valves shall be identified. All other valves installed in locations that are not adjacent to the fixture or appliance shall be identified, indicating the fixture or appliance served.

Full open valves are Ball or Gate type.
Shutoff valves are compression and any type.
In one and two family homes the IPC does not apply, rather, the IRC is applicable. Specifically, Section 2903. Each fixture (other than a bathtub or shower) is required to have accessible shut off valves either at the fixture or at the manifold.
 