I have tried to use the online wire sizing calculators and charts to determine what I am going to need and found that almost every calculator/chart gives a different answer.

120 Volts

Single Phase

Distance: 65 feet

Will be in conduit buried 18 inches

From the many calculators and charts I seem to be leaning toward these sizes and types for the following 3 loads...

1. 100 amp - #3 AWG THWN copper

2. 60 amp - #6 AWG THHN copper

3. 30 amp - #10 AWG THHN copper

Does the sizes and types look OK?
 

· Union Electrician
Joined
·
615 Posts
Yes. Some may say you'll need to bump the wire size for voltage drop, but IMHO I think those sound good. Assuming you are talking copper conductors.

Now don't forget about equipment grounding conductor size, and your pipe fill.
 

· Registered
Joined
·
8 Posts
Discussion Starter · #4 ·
I meant to type THWN for all of those. I'm glad you caught that. Those where copied and pasted directly from the shopping list I'm making and it was wrong there too.


1. 100 amp = #3 THWN copper

2. 60 amp = #6 THWN copper

3. 30 amp = #10 THWN copper

4. Ground = #6 THWN copper

PVC conduit, 40% fill, two 90 degree bends = 1 inch minimum. I'll go with 1 1/2" for easier pulling.
 

· Registered
Joined
·
1,769 Posts
I meant to type THWN for all of those. I'm glad you caught that. Those where copied and pasted directly from the shopping list I'm making and it was wrong there too.


1. 100 amp = #3 THWN copper

2. 60 amp = #6 THWN copper

3. 30 amp = #10 THWN copper

4. Ground = #6 THWN copper

PVC conduit, 40% fill, two 90 degree bends = 1 inch minimum. I'll go with 1 1/2" for easier pulling.
Go 2 inch in case you ever want to remove the wire and upgrade. The expense is the trench. The difference in pipe costs are negligible. Always go bigger with the pipe. Always.
 

· Licensed Electrical Cont.
Joined
·
7,829 Posts
Where could you possibly need 30, 60 or 100 amps at 120v???

If this is for a feeder you can and should use 240v for your calculations.

I agree, 65' is not even worth thinking about VD.
 

· Registered
Joined
·
272 Posts
I meant to type THWN for all of those. I'm glad you caught that. Those where copied and pasted directly from the shopping list I'm making and it was wrong there too.


1. 100 amp = #3 THWN copper

2. 60 amp = #6 THWN copper

3. 30 amp = #10 THWN copper

4. Ground = #6 THWN copper

PVC conduit, 40% fill, two 90 degree bends = 1 inch minimum. I'll go with 1 1/2" for easier pulling.

Are you saying you want to install ALL three of these circuits in your conduit, or that you are going to choose one from the list?

What is the circuit(s) for?
 

· Registered
Joined
·
1,125 Posts
is wire size right for load/distance?

IMHO the wire size/load calculations are correct. But adding in the other factor; Namely, distance. Even though the presented sizes are correct. But raising the size (AWG) (this is the funny thing about AWG. The higher the # the thinner the wire. Actually, it's not humorous at all. There's a logical reason for it. The gauge is measured from the outside IN. Therefore, the closer to the core, (higher #) the thinner the wire.) will increase performance, due to Voltage Drop!!!
 

· Registered
Joined
·
1,125 Posts
[Correct] wire-size? loads/VD

Where could you possibly need 30, 60 or 100 amps at 120v???

If this is for a feeder you can and should use 240v for your calculations.

I agree, 65' is not even worth thinking about VD.
You're right that 'feeder' calculations should be @ 240V. And @ 65ft., VD is not a major factor. But for individual loads the wire sizes are correct (theoretically). As far as increasing wire size; Even though Voltage drop is not a major factor @ less than 100ft+, still, it would improve performance! Again, the examples given here are mostly theoretical. With very little practical application!!!
 

· Licensed Electrical Cont.
Joined
·
7,829 Posts
IMHO the wire size/load calculations are correct. But adding in the other factor; Namely, distance. Even though the presented sizes are correct. But raising the size (AWG) will increase performance, due to Voltage Drop!!!
You really believe this at only 65 feet?
 

· Banned
Joined
·
5,990 Posts
The gauge is measured from the outside IN. Therefore, the closer to the core, (higher #) the thinner the wire.) will increase performance, due to Voltage Drop!!!
??
From Wiki
"Increasing gauge numbers give decreasing wire diameters, which is similar to many other non-metric gauging systems. This gauge system originated in the number of drawing operations used to produce a given gauge of wire. Very fine wire (for example, 30 gauge) requires more passes through the drawing dies than does 0 gauge wire"
 

· Registered
Joined
·
8 Posts
Discussion Starter · #13 ·
Are you saying you want to install ALL three of these circuits in your conduit, or that you are going to choose one from the list?

What is the circuit(s) for?
The wires are to be hard wired to a deck oven. The oven has two parts, an oven and a proofer.



Oven

240 volts
12250 watts
51 amps



Proofer

120 volts
2960 watts
24.6 amps



1. 100 amp = #3 THWN copper

One hot needs to be able to carry 51 + 24.6 amps = 75.6 amps


2. 60 amp = #6 THWN copper

One hot needs to be able to carry 51 amps.


3. 30 amp = #10 THWN copper

The neutral is only used in the 120 volt proofer part of the oven which runs at 24.6 amps.


4. Ground = #6 THWN copper

Then the ground wire for the entire thing.


 