I am thinking about replacing my water heater(died) with a tankless water heater and have a quick question about piping size. My house is piped with 3/4 inch PVC piping and the sales men at my local hardware store said the tankless water heaters they sell are 1/2 inch input and output. My question is will there be any problem converting down to 1/2 inch to go into the water heater and then back to 1/2 coming out of it as far as water pressure or anything like that? Any input would be great. Thank you.

jake
 

·
Experienced
Joined
·
2,885 Posts
There will be no problem reducing on the in and out, what you really have to consider is the size of the gas line to feed a tankless heater. All that I have seen require a 3/4" NG line, which will probably lead to issues with having enough gas/pressure for both your furnace and the tankless heater.

Mark
 

·
Registered
Joined
·
131 Posts
I agree with Jack.
Most residential water heaters are rated at 40,000 to 50,000 BTU's.
You tank less is going to be over 200,000 btu's. Not many home have that kind of excess capacity in the gas system.
 

·
Registered
Joined
·
3 Posts
Discussion Starter #4
Thanks for the fast post Mark. I asked the salesman about the gas line too. I have 1/2 inch NG pipe and he said the models they sell 'Eccotemp' are 1/2 inch. I was assuming I was good there but please let me know if I am wrong.

Thanks again.

jake
 

·
Registered
Joined
·
3 Posts
Discussion Starter #5
The model the guy was talking about is 'Eccotemp FVI-12-NG'. I have a 2 bed, 1 .5 bath home and he said this should be good. I normally don't do laundry or run the dishwasher together or when I'm taking a shower so that's what he recommended. It looks like its 74000 BTU so I'm hoping my current NG line will work. What do you guys think? It looks like it will be an easy install for me. I only need to modify a few things with the plumbing so my thought is if it doesn't work for me its only an hour or two.
 

·
Experienced
Joined
·
2,885 Posts
By the way hello Jake and welcome the best DIY'r site on the web.

Tankless heaters are rated for gpm at a given temperature rise, that being said I looked up a small eccotemp (3.5 gpm) and it was 75,000 btu's/hr.

The problem with that small a capacity is yes it will run from a 1/2" gas line as long as the line isn't too long, but if someone else in the home turns on the HW tap, the shower goes cold.

At a minimum a house with (4) peeps in it needs at least 7.5 gallons which would be more like 200,000 btu's/hr.

Mark
 