The pilot light is on the on position and is lit. However the burners do not light up. I checked the settings on the Aquastat they look good. the reset button on the Honeywell will not reset. I tried checking for the fuse but do not where it is located
 

·
Registered
Joined
·
99 Posts
It sounds like you have an older furnace, most older furnaces don't have a 3 amp fuse. Did you check for power to the furnace? Try to plug something in the outlet to see if it has power. If it has power, then you need to check the transformer for 24v. Try to reset the roll out switches. A roll out switch should have a button for you to reset. Here is a picture of the roll out switch
http://www.appliancezone.com/ShowProduct.aspx?ID=6776

if you press the roll-out switch and the furnace turns on, then you might have overheating problems.
 

·
Registered
Joined
·
99 Posts
eyesicon,

you sure the furnace is 3 years old? cause for a furnace to have a pilot light, it must be way older than that. Can you post the brand name, model and serial #. and when you said lit, is it lit all the time?
 