Payne 394jaw036045 furnace - not been used for over a year (was working before).
Pilot came on when call for heat, but furnace does not.
Gas valve is sx345ns0x2, it has 5 electrical terminals, terminal 2 is connected to terminal 3 with a black wire. 26VAC from 3 to 4 and 3 to 5, 0VAC from 1 to 2.
Valve terminal to the controller connection as follows:
Wire color----Controller----Valve terminal #
white---------- W ---------------1
yellow--------- Y ---------------4
green--------- GC --------------5
Is terminal 1 not getting the voltage to open the main gas valve?
If yes, what is the problem? Controller board?
Pilot came on when call for heat, but furnace does not.
Gas valve is sx345ns0x2, it has 5 electrical terminals, terminal 2 is connected to terminal 3 with a black wire. 26VAC from 3 to 4 and 3 to 5, 0VAC from 1 to 2.
Valve terminal to the controller connection as follows:
Wire color----Controller----Valve terminal #
white---------- W ---------------1
yellow--------- Y ---------------4
green--------- GC --------------5
Is terminal 1 not getting the voltage to open the main gas valve?
If yes, what is the problem? Controller board?