So I passed my rough inspection after I had to fix a few things. Here is what the inspector wrote up to be fixed prior to the re-inspection:
1. 6' or less to first receptacle in rooms
2. Receptacle required in hallway
3. Receptacles required within 6' or doorway and every 12' thereafter
4. GFCI required in all unfinished areas lower level
5. Smoke detector wiring
The receptacle within 6' of the doorway was for a bedroom that the first outlet on one side of the door was 6'7" measured linearly along the wall from the door, so I moved it about a foot closer to the door and was ok there. I took care of adding the outlet in the hallway, 2 additional outlets in the laundry/utility room that are not apart of the laundry circuit, and an outlet in the un-finished basement entry way. Wired up for 5 smoke detectors and one smoke/CO in the hallway. Passed the rough inspection this morning.
What is required for a final inspection other than all the outlets and switches being connected and installed? Do I screw all the outlets and switches into the box or leave them out for the inspector to see them? Do I make the final connections into the circuit panel before the final inspection? Just curious what they will be looking for on the final inspection trip....
1. 6' or less to first receptacle in rooms
2. Receptacle required in hallway
3. Receptacles required within 6' or doorway and every 12' thereafter
4. GFCI required in all unfinished areas lower level
5. Smoke detector wiring
The receptacle within 6' of the doorway was for a bedroom that the first outlet on one side of the door was 6'7" measured linearly along the wall from the door, so I moved it about a foot closer to the door and was ok there. I took care of adding the outlet in the hallway, 2 additional outlets in the laundry/utility room that are not apart of the laundry circuit, and an outlet in the un-finished basement entry way. Wired up for 5 smoke detectors and one smoke/CO in the hallway. Passed the rough inspection this morning.
What is required for a final inspection other than all the outlets and switches being connected and installed? Do I screw all the outlets and switches into the box or leave them out for the inspector to see them? Do I make the final connections into the circuit panel before the final inspection? Just curious what they will be looking for on the final inspection trip....