Id like to clarify the purpose of ground rods.
Ground rods in normal residential structures are NOT for lightning protection or to provide a "Ground fault path"
ALL they do (during normal usage) is stabilize the voltage to ground. They do ABSOLUTELY NOTHING MORE. It also creates a network (between the xformer ground, system neutral, and your neighbors ground rods....) to stabilize voltage and provide a redundant return path....
Think of it this way: every point along the earths surface has a different voltage potential. Your outbuilding approx 100 feet away lets say has a different voltage potential. So therefore you run a separate ground wire (to provide a current return path) and a new ground rod (to prevent a voltage difference on your outbuilings ground system) Lets say you touch an object connected to your system ground. You are touching a grounded object with the voltage potential of your main system panel, NOT the geographic location you are at. Therefore by driving a ground rod it stabilizes this voltage difference between two different geographic locations. The same applies with your main structure ground rod, it stabilizes the voltage between the transformers ground wire and your structures physical location (a few hundred to a few thousand)
Now, in the event you lose your system neutral, They become a higher impedance ground that is a fail safe. It creates a path to ground, HOWEVER it is NOT a replacement, as it has a much higher resistance to get the current to ground.
THIS MEANS: if you lose your system neutral, and your ground rods/water system bonding become your neutral path, you most likely will get lightly shocked should you touch the metal case of something in your home......
Take an Ammeter to your copper bare ground wires.....get a decent amount of unbalanced loads going and meter your system neutral, bonding copper for your water system and your ground wire....the majority of your current should be going through your system neutral as it is the lowest impedance return path.
I hope this helps everyone understand the purpose of ground rods......