the Musigician
Joined
·
10,404 Posts
Wire-nutted extensions INSIDE the panel are allowed, I do believe.

DM
 

·
Banned
Joined
·
17,158 Posts
What you really need to do, is go buy a Wire Stretcher.

Danger mouse, it depends on local AHJ if they like that as a fix or not. Some frown on that practice, especially if they have a hair up their rear when inspecting home owner builds or mods to a system.
 

·
Super Moderator
Joined
·
9,335 Posts
What you really need to do, is go buy a Wire Stretcher.

Danger mouse, it depends on local AHJ if they like that as a fix or not. Some frown on that practice, especially if they have a hair up their rear when inspecting home owner builds or mods to a system.
They may frown on it, but unless a local code prohibits, the NEC allows it.
 
  • Like
Reactions: DangerMouse

·
Registered
Joined
·
9,477 Posts
What you really need to do, is go buy a Wire Stretcher..
1. When you stretch a wire, it gets thinner and therefore won't carry as many amperes.
2. It is impossible to grip the last few feet of a current carrying conductor and stretch it without breaking the insulation.

It is okay to splice on a short length of wire (a pigtail) so the circuit whose wire is already inside the panel can be connected the terminal you want.
 