I have a 4 wire oven and 4 wires from the homerun is it electrically safe if I put the grounding together and have it grounded to the junction box or should I just connect the groundings together and put a wire cap on it or are either of those fine?
 

·
Licensed Electrician
Joined
·
4,352 Posts
If the junction box is metal it is required to be bonded.
 
  • Like
Reactions: NJMarine

·
Semi-Pro Electro-Geek
Joined
·
3,403 Posts
So it's required to be grounded to the box?
The box is required to be grounded. The oven is also required to be grounded. So both the oven and the box need to be connected to the grounding conductor.
 