If your indoor fan and condenser fan is running when the thermostat is calling for cooling then you don't have a low voltage problem.
You either have a bad compressor capacitor, compressor issue-open circuit, loose conection but more than likely you don't have 220vac going through the contactor and the contactor needs to be replaced. Check voltage going into the contactor and out of the contactor while the contactor is pulled in. If it is 220 going in and out then it's time to check the capacitor and then the compressor.
Good luck
You either have a bad compressor capacitor, compressor issue-open circuit, loose conection but more than likely you don't have 220vac going through the contactor and the contactor needs to be replaced. Check voltage going into the contactor and out of the contactor while the contactor is pulled in. If it is 220 going in and out then it's time to check the capacitor and then the compressor.