That's a good question... and I have met a lot of GC's that wouldn't know the answer but some, maybe most, wouldn't care either. I give you one up for that.
The only way a voltage drop occurrs on a circuit is when a current is flowing. Ohms law backs that up. For current to flow, there must be a resistance across conductors of different voltage potential. A poor connection in series with such a circuit will drop part of the original voltage across the poor connection and the remainder across the device used for measuring it (or any other resistance in parallel).
For example, if the measuring device had no resistance at all, then the circuit could have an extremely poor connection and still measure full voltage.? That is never quite the case... even the digital voltmeters have an input resistance, albeit quite high. They are often referred to as "high Z" or "high impedance" meters. Some of the more expensive ones have a "low Z" setting to use when in doubt about the possibility of being fooled with ghost reading when measuring a high impedance circuit (one with a high resistance connection for example). That's where the strange voltage reading come into play. That's why on crude electrical work, a digital voltmeter isn't often the best way to get a useful reading.
An analog meter with lower input resistance will give more useful reading for common circuits that most electricians will encounter. A cheap analog meter is one choice. The trusty "Wiggy", which is an electrical solenoid type volt measurement device with a built in growler is a good choice for carrying in the pouch. It's bullet proof and has a scale the shows all the voltages you will ordinarily come across. It loads the circuit even more than the analog meter.
The lower the input resistance of the measuring device, the more the voltage will drop across the poor connection in the circuit. Ohms law at work as always.
Now as to a pour connection, that sounds like someone you may know who works at a winery. :biggrin2:
Surf..... AGREE and thanks........
(I could not understand your answer to my question and then I went back and read my question parameters....I typed
low impedance for the meter, when I meant
high resistance/impedence. like most MMs, (and no other load on the circuit except normal wire resistance and a poor connection.))
Maybe, no not maybe, I had a couple of pours tonight.:smile:
To me, given a high impedance MM, and no load on the circuit, seemed a 35V drop was a lot of drop for just a loose connection. Do you think so.????
Couple that with the fact that the circuit had been fine before, and the OP did OTHER wiring in the circuiut, and had not touched that box/connection he said was loose, ........it made me wonder if perhaps he had lost a neutral somewhere else and got two legs in series and was measuring with a load on.
It just seemed like 35V was a lot of drop for a poor connection read with a high impedience MM. Maybe not....Again I'm a GC with more than a couple of pours tomoght.:wink2::smile::smile::smile:
Best...I'm probably still mixed up.