· Super Moderator
Joined
·
8,658 Posts
Yes in most cases, it will be ungrounded but will prevent against shocks. Idk about 50's wiring though. Insulation must be crumbling off the wire by now.

how did you ever get an insurance company to insure the house? lol.


I'm sure the house has been rewired at some point . so you should be fine.


Yes there are plenty of videos out there showing how to do this step by step.
 

· Registered
Joined
·
8,116 Posts
Oldmaster is exactly right. Identify hot and neutral and connect accordingly.
 

· Registered
Joined
·
701 Posts
You may have BX or armored cable. If it is terminated correctly you my have a functional ground. With a voltmeter check from the hot wire to the cable sheath. If it's a metal box and the cable is under the cable connectors you may be good. Worth a try.
 

· Registered
Joined
·
1,162 Posts
SeeThis1!:
The other thing you should be aware of before it drives you nuts is that if you are installing GFCI receptacles and they will not be grounded (which is perfectly fine and they will function to protect from personal injury) keep in mind though that if the GFCI is not grounded using a plug in tester will not trip the GFCI. This is normal if the GFCI is not grounded. Pressing the test button on the GFCI itself will test it. So if you use a plug in tester and it won't trip the GFCI don't think you did something wrong. As long as the test button trips it you are good.
 

· Super Moderator
Joined
·
18,307 Posts
You may have BX or armored cable. If it is terminated correctly you my have a functional ground. With a voltmeter check from the hot wire to the cable sheath. If it's a metal box and the cable is under the cable connectors you may be good. Worth a try.
Even AC without the bond wire will show as a ground. Without the bond wire AC is not an acceptable grounding means.
 

· Registered
Joined
·
1,344 Posts
If BX outer armor shield is grounded to a metal box (screw clamp outside box, locking 'O' nut inside box), isn't box then grounded? If yes, can't ground wire on GFI get attached to any available screw that is part of box?
 

· DIY Veteran
Joined
·
711 Posts
My father's house was built in '57, has the braided cloth insulation on the wires. in pretty bad shape now. He updated a lot of it and installed breakers but not the wiring behind the plaster walls.
Use common sense...
 

· Super Moderator
Joined
·
18,307 Posts
In AC cable the internal bonding strip is not the equipment grounding conductor. The armor is the equipment grounding conductor. It is important to use the correct connectors to maintain the integrity of the grounding system.
The armor is only an egc if the bond strip is in place. The resistance can be too high without it.
 

· Super Moderator
Joined
·
18,307 Posts
In bx there is no internal bond wire. Theoretically the bx outer interlocking armor is tight enough to maintain grounding integrity.
Wrong. .

Early versions did not have it. Newer versions do have the bond strip, even today.
 

· Registered
Joined
·
701 Posts
I think sometimes we create issues with the terminology we use. Notice there is no mention of "BX" cable in the NEC. In reality most people refer to AC and MC cable as "BX". In a time past there was a true BX but not for many years.
 

· Registered
Joined
·
9,460 Posts
You should be aware of the difference between GFCI and "grounding". I once had an electrician, who referred to himself as a "master electrician" (whatever that is), tell me the GFCI won't work without a ground wire. Just shows you can't always trust an electrician either.


GFCI can't "make up" for a missing ground wire. It can't turn an ungrounded outlet into a grounded outlet.


What grounding does is supply a path for electricity to flow if it finds its way out of the normal path in a fixture. For example, if you have a lamp or power tool plugged in, and there is an internal failure, for example a loose wire inside touches the exterior metal part of the lamp, then that current will be shunted down the ground wire, if the lamp is properly grounded.


A different situation is when there is something external - such as water for example - that can be a path for electricity. For example you're standing in a puddle in your lawn and you touch a hot wire, or a metal casing on a tool that is touching a hot wire. In this case the GFCI circuit will detect that more current in coming into the hot side than is leaving the neutral side, and it shuts it off. Grounding will not protect you in this case.


GFCI will not protect you from getting electrocuted. It only protects you from current leaving the circuit. For example if you stick a key in the right slot of an outlet and a key in the left slot, and then grab on with your right and left hands, the GFCI is not going to turn off because current in = current out.


I'm sure you can imagine other scenarios and all points in between, but the bottom line is the GFCI and "grounding" do 2 different things.
 