DIY Home Improvement Forum banner
1 - 9 of 9 Posts

· Registered
Joined
·
11 Posts
Discussion Starter · #1 ·
This problem just came up - outlet been working fine for 20 years. I have an open neutral on just the one outlet in my laundry room. I pulled the outlet out - just one black wire, one white wire and a ground. Changed out the outlet - no difference. My furnace also runs on this circuit and it's working fine - can't find anything else.


I checked voltage at the wires coming to the outlet - black to ground, I have 124 volts - white to ground, I have 17 volts.


Any suggestions?


Thank you,
ryan
 

· Super Moderator
Joined
·
8,669 Posts
Check the basic stuff first. If furnace is on that circuit, look for a junction box or other outlets. Check all wire nuts, maybe a neutral wire came loose somewhere at a terminal or wire nut. Just a suggestion.
 

· wNCmountainCabin
Joined
·
205 Posts
are you 'sure' the furnace is on this SAME circuit? trip the circuit breaker and see if the furnace still works - an easy test.

if so, and you are certain your 'tester' is working(test in other outlets, too), then yes, you have a loose/lost neutral somewhere back to the panel... (or, is there a chance there is actually another outlet on this circuit, maybe behind the washer room?)
 

· Registered
Joined
·
11 Posts
Discussion Starter · #6 ·
Problem has been solved! Loose white wire connection in the panel - screw had backed out so far in the bus, wasn't even making contact with the wire. Tightened it down - and the rest of them at the same time - and everything is in order.


Things are not usually this easy for me...but I'll take it!


Thanks, ryan
 