Discussion Starter · #1 · (Edited)
Hello gang. My old Carrier 38YR036320 heat pump is completely frosting over. The ice is quite thick, both on the inside and the outside of the coil. The fan runs just fine. See attached photo. I am in southern Illinois and right now our outdoor temps are ranging from 55 deg to 27 deg. We bought the house a year ago. Shortly after the purchase, we had a trusted local HVAC tech look at it, as a prevetionative maintenance check. He added one pound of R22 and replaced the aux heat sequencer, which had a burned relay.

Last spring I installed a new/used thermostat, a Honeywell TH8320U1008, which I had removed from the house we just sold. I have installed the optional outdoor sensor. When wiring the stat, I used the "2H/1C Heat Pump (with aux heat)" wiring table

The aux heat seems to be working fine, and the house is coming up to temp in the morning.

When I first discovered the frosting on the unit, I switched the thermostat the A/C and it quickly defrosted.

Is there something I could check before I have to call the tech? I do have a digital multi-meter.

I am also concerned that I may have some settings wrong on the stat. Could it have something to do with the O/B changeover valve? Perhaps the compressor lockout temps?
My settings follow:
0170 7
0190 0
0200 0
0220 3
0250 9
0270 9
0300 1
0310 3
0320 0
0340 2
0350 20
0360 40
0530 1
0600 80
0610 50
0650 0
0660 0
0680 2
0690 2

Thanks for the help.
 

Attachments

·
Registered
Joined
·
569 Posts
Looks like a problem with the unit itself not going into defrost. The thermostat has nothing to do with the defrost cycle and as long as it cools in the summer and heats in the winter, than you have the changeover o/b set properly.
probably should just call someone out to look at it.
 

·
Registered
Joined
·
37,410 Posts
Three things I know of that can cause it, Low freon, lack of air flow (dirty coil or air filters) and a bad defrost valve.
 

·
I'm Your Huckleberry
Joined
·
5,884 Posts
I was about to say one pound of refrigerant is quite a bit to add. I'd call him back out to see where the levels are at now and if it's near or over in need of a pound than have him find and repair the leak.

No such thing as a defrost valve, only a defrost board. I think that's what joe meant.

Reversing valve should receive 24 volts during a call for cool on yours.
 

·
Registered
Joined
·
191 Posts
Discussion Starter · #6 ·
I think I found the problem - and the repair is outside of my skill set.

Like I said, it's an old heat pump. I took the cover off to take a couple of photos to show you guys. First, I discovered a dial sort of thing, with degree markings on it. Then I looked closer, and I saw it had a very fine capillary tube coming out of it. Looking some more, the tube didn't seem to be connected to anything. Looking some more, I saw a couple of grooves worn in the 1/2" copper tube that it was apparently supposed to be connected to.

I gather that this tube provides some kind of temperature input to the dial gizmo. How was it originally attached? Secured with a wire tie? Soldered? trapped under now missing insulation?

I guess it's time to call in the cavalry.
 

Attachments

·
Registered
Joined
·
569 Posts
That dial you are refering to is an outdoor thermostat for either locking out the heat strips above a certain temp, or locking out the compressor below a certain temp.
The unit doesnt appear to be old per say as you keep refering, I wouldnt say much more than 10 years but at the same time, I'm more familliar with all in one package units.
I also would say the reversing valve was working fine, as you say you switched it over to a/c and it defrosted.
I would say in my opinion, either you had a bad defrost board, or bad defrost sensor which is a small thermostat mounted in the bottom portion of the unit. From what I've seen, usually the latter.
 

·
Registered
Joined
·
191 Posts
Discussion Starter · #8 · (Edited)
That dial you are refering to is an outdoor thermostat for either locking out the heat strips above a certain temp, or locking out the compressor below a certain temp.
The unit doesnt appear to be old per say as you keep referring, I wouldnt say much more than 10 years but at the same time, I'm more familliar with all in one package units.
I also would say the reversing valve was working fine, as you say you switched it over to a/c and it defrosted.
I would say in my opinion, either you had a bad defrost board, or bad defrost sensor which is a small thermostat mounted in the bottom portion of the unit. From what I've seen, usually the latter.
The S.N. is 3893E0352, which I understands means it was manufactured in the 38th week of 1993, putting it at 19 years old?

The only board I've seen is the one in the photo. Would that be the defrost board?

What would the defrost sensor look like? Would it be a copper tube or a wire thermocouple?

I have my HVAC guy coming on Monday morning.
 

·
Registered
Joined
·
191 Posts
Discussion Starter · #10 · (Edited)
I would seriously consider just replacing a 21 year old heat pump for one that has a higher hspf.
I understand. However, when we just bought the house, we had an energy audit done. The auditor did his thing and said the payback for a new unit would be well over 10 years. So, as long as the thing is basically working right, we'll continue to have it serviced.

Maybe it will go TU in a short period of time, but if I can continue to have once-a-year service calls of less than $200 or so, we'll hang on to it.

I appreciate your thoughts, though.

BTW, I located the correct Carrier troubleshooting destructions for the defrost board and outdoor coil thermostat. I'll run through those checks this afternoon.
 

·
Registered
Joined
·
191 Posts
Discussion Starter · #11 · (Edited)
I went through some of the diagnosticcs. First the outside coil thermostat.

It seemed a bit loose on the coil. I wiggled it around a bit and cleaned out the leaves around it.

The manual has you disconnect the thermostat and put a meter on it. It should be a short below 30 deg and infinity above 80 degrees.
I came up with short at the cold temp, and about 1.5 Meg ohms at the higher temp. I assume that is okay.

Then it has you jumper where the thermostat was and run the unit. They have you place a screwdriver on a shorting lug on the board. I heard the valve operate.

Unit is now operating in defrost mode. Check between C and W2 using voltmeter as shown in Fig. 21. Reading on voltmeter should indicate 24v. This step ensures defrost-relay contacts have closed, energizing supplemental heat (W2) and reversing-valve solenoid (O).​

When I placed my meter across C & W2, I was only getting about 23 mV, not 24V. At first I thought it must be a bad control board. But then I remembered I installed a different thermostat and wonder if I am missing some kind of input to the board. Why, I wonder, am I not getting the 24V? The board p.n. is CES0110063 and it shows up on Google searched. About $55.00

Looking at the thermostat wires, W2 goes to the Aux terminal on the thermostat. C appears to be a common?

I'm pretty sure the heat pump is a 2H/1C. and except for the heavy frost, it seems to be working correctly.

:bangin:
 

·
Registered
Joined
·
23 Posts
No, that "dial" is a Ranco E15 electromechanical defrost timer

rather than a defrost board as todays units have, yesterdays heat pumps used the Ranco E 15 defrost timer.
The sensing bulb is the defrost terminator or tstat.
The Ranco E15 can be set to search for a defrost condition every 30/60/90/120 mins, amd the sensing bulb will close the defrost termination switch in the timer to signify a defrost condition exists and when the timer searches next time it will initiate a defrost cycle, either until the temp is reached and opens the defrost terminators switch or the duration of the defrost timed cyle expires, the terminator insures it will only defrost if needed and only as much as required.
To troubleshoot this timer 1st you need to manually close the temp switch on the timer, after thats done manually advance the timer until it clicks this will initiate the defrost cycle. You can simply run the AC mode to see if the reversing valves working for the defrost modes, the reversing valves get tired as dothe compressors and low refrigerant will do this as well.
 

·
Registered
Joined
·
569 Posts
rather than a defrost board as todays units have, yesterdays heat pumps used the Ranco E 15 defrost timer.
The sensing bulb is the defrost terminator or tstat.
The Ranco E15 can be set to search for a defrost condition every 30/60/90/120 mins, amd the sensing bulb will close the defrost termination switch in the timer to signify a defrost condition exists and when the timer searches next time it will initiate a defrost cycle, either until the temp is reached and opens the defrost terminators switch or the duration of the defrost timed cyle expires, the terminator insures it will only defrost if needed and only as much as required.
To troubleshoot this timer 1st you need to manually close the temp switch on the timer, after thats done manually advance the timer until it clicks this will initiate the defrost cycle. You can simply run the AC mode to see if the reversing valves working for the defrost modes, the reversing valves get tired as dothe compressors and low refrigerant will do this as well.
He doesnt have the old setup.
 

·
Registered
Joined
·
23 Posts
I see Ranco E15 timer clear as daylight

The dial thing he calls it with the sensing buldb is the defrost timer!

The defrost works the same on heat pumps, refrigerators etc.
Its "TIME AND TEMPERATURE" initiated and
its " TIME OR TEMPERATURE" terminated!
Meaning both time and temp must be present to initiate a defrost and either one alone, time or temp dropping out will terminate the defrost cycle.
The sensing bulb is the temperature aspect and the timer is the time.
 

·
Registered
Joined
·
23 Posts
This is what the upgraded defrost board looks like

<a href="http://tinypic.com?ref=25zm6c6" target="_blank"><img src="http://i49.tinypic.com/25zm6c6.jpg" border="0" alt="Image and video hosting by TinyPic"></a>

it needs no Ranco E15 to go with it.
 

Attachments

·
Registered
Joined
·
23 Posts
OOOPS old eyes got me, I hate getting old!

That sucker looked just like a Ranco until i actually saw it blown up pathetically large on my monitor, wow that is only a 2nd stage/auxillary heat strip tstat, My bad sorry. but the same goes as to theory /troubleshooting there are 2 ternminals the defrost terminator wires to saying dt usually or temp
and the 2 pins you short are usually saying test under them, you jumper both the temp and test terminals to initiate a defrost, which is the AC mode sans outdoor fan. the ohms readings are either a reading being closed or infinite being open any reading beyond infinite = a continuity or no reading whatsoever will be ead as in infinite=open.

I would 1st see how the units runs inthe AC mode, and if the discharge line at the compressor is cool enough to grab onto its got issues, either low gas or reversing valve and or compressors volumetric efficiency/compression is down.
The high side will be 270# and the low side around 65-70 depending on heat load /humidity and outdoor temps, ambient + 3- degrees is the condensing temp by design, converted to pressure for R22 = 70 psi @ 40F and 270psi @ 130F
 

·
Administrator
Joined
·
41,937 Posts
The dial thing he calls it with the sensing buldb is the defrost timer!

The defrost works the same on heat pumps, refrigerators etc.
Its "TIME AND TEMPERATURE" initiated and
its " TIME OR TEMPERATURE" terminated!
Meaning both time and temp must be present to initiate a defrost and either one alone, time or temp dropping out will terminate the defrost cycle.
The sensing bulb is the temperature aspect and the timer is the time.
Looks like a standard Ranco outdoor thermostat, not an E15 defrost control.


OP, even if your defrost board isn't putting out 24 volts to your aux heat terminals, you have more problems then that. Good chance its a bit low on charge again, or when that teh added 1 pound, he over charged it.
 

·
Registered
Joined
·
191 Posts
Discussion Starter · #19 ·
Thanks for all the input fellas. Please take another look at that "dial thingy" I have in post #6. It's blurry because this forum restricts files over than 100 kb.

Anyhoo, I see in my clear copy of the photo that it is a Dayton Electric model 2E552. When I do a Google search for this item I see there is supposed to be a bulb on the end of the capillary tube. For example: http://www.plccenter.com/en-US/Buy/DAYTON/2E552 So, I don't think it's a Ranco E15, but a Dayton 2E552.

Now look at the third photo photo in post #6 above. That thin tube comes from the Dayton 2E552 and the bulb is missing!!! Inside the unit, the capillary tube is wound up in a 3" coil. It looks like the bulb-end chafed against the larger tube, show in the photo, and it wore through and fell off. I haven't located the bulb.

This can't have a positive effect on the operation of the heat pump.

If I buy a new Dayton unit, where should the bulb be placed? In free air inside of the unit?
 

·
Administrator
Joined
·
41,937 Posts
Its not needed. It was most likely used to lock out your aux heat. Since you have the TH8320 with an outdoor sensor, it takes place of that outdoor stat. You can wire the 2 wires attached to it together. Verify that it is only being used to lock out your aux heat first.
 