Hi guys
I guess this is my heating week
You just helped me with my sons second zone issue, now I have one of my own.
I'm glad it's still warm here so there is no pressure.
I have an older Beckett that's giving me trouble. It's on an old arcoliner boiler, 3 zone hot water.
I recently serviced the unit- vacuum, nozzle, filters, adjusted with older FYRITE. etc.
It has been running fine for a couple of months until now
It might run all day and then again it might not fire. it starts instantly when the reset button is pushed.
I have cleaned the cad eye, i have reset the electrodes.
Three years ago this unit was under 4 feet of water from sandy. I put in a new motor and it has been running fine till now. I suspect the primary is the problem. it's an old honeywell gray box.
Is there any way to test this control.?
I have been looking for a replacement but I can't find an exact duplicate.
I know that this has constant ignition because when I lift the transformer when it's running it's arcing.
Am I headed in the right direction.
which control would work as a replacement.
or should I scrap it and put in a new Beckett I can pick up for about $400
Thanks in advance
Ralph
I guess this is my heating week
You just helped me with my sons second zone issue, now I have one of my own.
I'm glad it's still warm here so there is no pressure.
I have an older Beckett that's giving me trouble. It's on an old arcoliner boiler, 3 zone hot water.
I recently serviced the unit- vacuum, nozzle, filters, adjusted with older FYRITE. etc.
It has been running fine for a couple of months until now
It might run all day and then again it might not fire. it starts instantly when the reset button is pushed.
I have cleaned the cad eye, i have reset the electrodes.
Three years ago this unit was under 4 feet of water from sandy. I put in a new motor and it has been running fine till now. I suspect the primary is the problem. it's an old honeywell gray box.
Is there any way to test this control.?
I have been looking for a replacement but I can't find an exact duplicate.
I know that this has constant ignition because when I lift the transformer when it's running it's arcing.
Am I headed in the right direction.
which control would work as a replacement.
or should I scrap it and put in a new Beckett I can pick up for about $400
Thanks in advance
Ralph