old wiring

1575 Views 4 Replies 4 Participants Last post by  InPhase277
Hello,

until I can upgrade my wiring I have a question...I have old cloth type wiring with no ground and my question is all my outlets are old school with only two prongs can I upgrade the outlets and not having the ground wire hurt any of my fixtures and washer/dryer?

Thanks

Z
1 - 5 of 5 Posts

· Registered
Joined
·
64 Posts
You could put GFCI outlets, you would only need one at the beginning of the circuit and all the outlets connected to the load side of the GFCI will be protected, you should also place the "No Equipment Ground" label on the outlets that come after the GFCI.
 

· Registered
Joined
·
31 Posts
Discussion Starter · #4 ·
You could put GFCI outlets, you would only need one at the beginning of the circuit and all the outlets connected to the load side of the GFCI will be protected, you should also place the "No Equipment Ground" label on the outlets that come after the GFCI.

Thanks for the response......This is an old cinder block house so all outlets run from a j-box in the attic down wall seperatly,can I put in some type of gfci breaker and then just change outlets with regular 15a?
 
1 - 5 of 5 Posts
This is an older thread, you may not receive a response, and could be reviving an old thread. Please consider creating a new thread.