OK, the white wire going from the lighting fixture should be connected to the HOT (not the black wire), and the black wire coming back from the switch should be connected to the fixture.
I did have that wrong, code reference below:
200.7 (C) (1)
Exception (1)
If part of a cable assembly that has the insulation permanently reindentified to indicate its use as an ungrounded conductor by marking tape, painting, or other effective means at its termination and at each location where the conductor is visible and accessible. Identification shall encircle the insulation and shall be a color other than white, gray, or green. If used for single-pole, 3-way, or 4-way switch loops, the reidentified conductor with white or gray insulation or three continuous white stripes shall be used only for the supply to the switch, but not as a return conductor from the switch to the outlet.