Discussion Starter · #1 ·
In an old house I tried to put a wall switch in the bathroom. Got the new wire run and ready to hook up but I noe realize I only have two wires one coming in the box and one going out of the box. I don't know what to do. Help
 

· Registered
Joined
·
350 Posts
I'm assuming you have 2 wires coming in and out of a light fixture box?
Should be 1 hot and 1 neutral.
You need to switch the HOT conductor, not the neutral conductor.
The neurtal stays connected to the light, the hot wire coming into the box connects to the black wire going to the new switch. At the switch, the black wire connects to one screw on the switch, and the white to the other screw. THE WHITE MUST BE RE-IDENTIFIED AS A HOT CONDUCTOR. This is done by wrapping black electrical tape around the white wire in at least one place, the tape must completely encircle the wire. At the light fixture, you attach the white wire from the switch to the old hot terminal on the fixture. The white wire MUST be identified as a hot here also.

If you are not comfortable doing this, or identifying the hot conductor, you really should have an electrician hook it up for you, especially in a bathroom where things get wet.
 

· Registered
Joined
·
37,499 Posts
The info posted could not be more wrong.
Please hold in there for a real electrition to post the right ansewer.
 

· Registered
Joined
·
350 Posts
Please correct me then, I believe I did give a good answer, if not I will gladly edit and correct it or completely delete it.
It is never my intension to give bad , misleading, or incorrect information, never.
 

· Licensed Electrician
Joined
·
4,352 Posts
I'm not fully understanding why you ran a new wire, is it to feed another switch, or simply another light using the existing switch?

Either way, it sounds to me like you either have knob and tube wiring or a switch loop. Either way, you will not be able to extend this wiring to feed something else.

Edit...You need to be more specific with what you are trying to do and what is already existing.
 
  • Like
Reactions: joecaption

· Registered
Joined
·
350 Posts
OK, the white wire going from the lighting fixture should be connected to the HOT (not the black wire), and the black wire coming back from the switch should be connected to the fixture.

I did have that wrong, code reference below:

200.7 (C) (1)

Exception (1)
If part of a cable assembly that has the insulation permanently reindentified to indicate its use as an ungrounded conductor by marking tape, painting, or other effective means at its termination and at each location where the conductor is visible and accessible. Identification shall encircle the insulation and shall be a color other than white, gray, or green. If used for single-pole, 3-way, or 4-way switch loops, the reidentified conductor with white or gray insulation or three continuous white stripes shall be used only for the supply to the switch, but not as a return conductor from the switch to the outlet.
 
  • Like
Reactions: jbfan

· Registered
Joined
·
6 Posts
Discussion Starter · #11 ·
I'm not fully understanding why you ran a new wire, is it to feed another switch, or simply another light using the existing switch?

Either way, it sounds to me like you either have knob and tube wiring or a switch loop. Either way, you will not be able to extend this wiring to feed something else.

Edit...You need to be more specific with what you are trying to do and what is already existing.
There was a light with only a pull chain switch. I am trying to install a wall switch. There is only one single wire coming in the box and one single wire going out of the box. I am comfortable with most wiring but not this situation. Thank you for your response.
 

· Registered
Joined
·
6 Posts
Discussion Starter · #12 ·
old house wiring

There was not a wall switch. Only a pull chain from the light socket. I am trying to run a wall switch. There is only one single wire coming into the light box and one single wire going out. Thus my problem
 

· Registered
Joined
·
350 Posts
 

· Registered
Joined
·
199 Posts
So, you have an unswitched light (has a pull chain but that's fixture mounted) on a box with 2 wires in it. One wire will be hot, the other neutral. You would put a switch loop on the hot leg in that box and make sure to relabel the white wire as mentioned because it becomes a hot wire.
 

· Registered
Joined
·
6 Posts
Discussion Starter · #16 ·
SuperJETT, Idon't have a black and white wire coming in the box. I only have one single wire in and one single wire out. I hope I have explained this in the right manor. Thank you for your quick response.
 

· Registered
Joined
·
350 Posts
SuperJETT, Idon't have a black and white wire coming in the box. I only have one single wire in and one single wire out. I hope I have explained this in the right manor. Thank you for your quick response.
Yes, I understand. In newer wiring, one of those wires would be colored black (hot), and one would be colored white (neutral).

Both of yours are black but one of them is a hot and the other one is a neutral.

The next thing to do is to determine which one is which. You can do this with a meter, or a simple electrical tester.

Do you have a tester?
 

· Registered
Joined
·
350 Posts
Glad to hear it!
 