I have to share my unattended monitor system I use for systems that have intermittent problems that can be caused by one of the various safety switches in modern systems triggering random shutdowns. It's not a substitute for a Tektronix digital scope with single shot recording but it doesn't cost 4 grand either.
I sacrificed an old Christmas tree light string and made a few "Test Lights" using the sockets and the pigtails they provided and put some small insulated alligator clips on them.
Since they have 2.5 volt bulbs in them, which is standard for a 50 bulb series incandescent string, I connect these across any suspected normally closed switch, such as roll out, high pressure, low pressure, high temperature... etc. that can open to cause a system shut down. If the switch opens, this poor little bulb becomes a tiny flash bulb, never to burn again. You can even use it on a normally open pressure switch if you hook it up shortly after startup but would only be good for one session of course.
I can go about my other business and still know which/if any of the safety switches caused the shutdown. I can leave them connected for days at a time waiting for the elusive intermittent problem to sneak up once more.
Now I'm not saying that means the device that blew the bulb is the problem, but it can point me in the right direction. Sure, you can use any error codes that a sophisticated board may be generating but some boards don't do that and sometimes you may not have access to what the code means. There are applications beyond HVAC as well.
I used another version of this same logic one time to see which parking lot light, on a string of 4 that shared the same circuit, was intermittently shorting and tripping the breaker. I put marginally rated fuses in the load line of each light and voila! The one that blew the fuse turned out to have a bad striker in it that was going bonkers on rare occasions and causing the ballast inrush current to overload the circuit just enough to trip the branch breaker.
These methods may not be for you but they have saved me lots of time and allowed me to fix things that the other guys couldn't do. That enabled me to make the big bucks and retire and while away the hours on some DIY site. :biggrin2: And yes, I did have a Tektronix scope but I saved it for the rare occasion when the light Christmas light method failed me... not often
You sometimes have to take unusual measures to diagnose unusual problems. I think the best diagnostic tool available is often right between your ears. My grandpa used to put a horsehair on the doorknob of his blacksmith shop to see if anybody was in the shop while he was away. I always wondered how he knew I was in there... he never revealed his method until I was fully grown and we laughed about it. I miss him.
Thanks for reading if you made it this far.
Best regards, SD2
I sacrificed an old Christmas tree light string and made a few "Test Lights" using the sockets and the pigtails they provided and put some small insulated alligator clips on them.
Since they have 2.5 volt bulbs in them, which is standard for a 50 bulb series incandescent string, I connect these across any suspected normally closed switch, such as roll out, high pressure, low pressure, high temperature... etc. that can open to cause a system shut down. If the switch opens, this poor little bulb becomes a tiny flash bulb, never to burn again. You can even use it on a normally open pressure switch if you hook it up shortly after startup but would only be good for one session of course.
I can go about my other business and still know which/if any of the safety switches caused the shutdown. I can leave them connected for days at a time waiting for the elusive intermittent problem to sneak up once more.
Now I'm not saying that means the device that blew the bulb is the problem, but it can point me in the right direction. Sure, you can use any error codes that a sophisticated board may be generating but some boards don't do that and sometimes you may not have access to what the code means. There are applications beyond HVAC as well.
I used another version of this same logic one time to see which parking lot light, on a string of 4 that shared the same circuit, was intermittently shorting and tripping the breaker. I put marginally rated fuses in the load line of each light and voila! The one that blew the fuse turned out to have a bad striker in it that was going bonkers on rare occasions and causing the ballast inrush current to overload the circuit just enough to trip the branch breaker.
These methods may not be for you but they have saved me lots of time and allowed me to fix things that the other guys couldn't do. That enabled me to make the big bucks and retire and while away the hours on some DIY site. :biggrin2: And yes, I did have a Tektronix scope but I saved it for the rare occasion when the light Christmas light method failed me... not often
You sometimes have to take unusual measures to diagnose unusual problems. I think the best diagnostic tool available is often right between your ears. My grandpa used to put a horsehair on the doorknob of his blacksmith shop to see if anybody was in the shop while he was away. I always wondered how he knew I was in there... he never revealed his method until I was fully grown and we laughed about it. I miss him.
Thanks for reading if you made it this far.