How many devices can be on one circuit. I am in upstate New York. Is there a limit like in Canada? I have six recessed cans, three under cab light sections and two pendants. All will be led except cfl's in the pendants.

Thanks,
Eric
 

· Licensed Electrician
Joined
·
4,352 Posts
There is no set limit in the NEC. There may be a local or state limit. There is a limit (I think) of 11 in Canada.
 
  • Like
Reactions: Ebierley

· " Euro " electrician
Joined
·
5,369 Posts
How many devices can be on one circuit. I am in upstate New York. Is there a limit like in Canada? I have six recessed cans, three under cab light sections and two pendants. All will be led except cfl's in the pendants.

Thanks,
Eric
In usa side there is no limit AFAIK., but in Canada side., Oui there is limit 12 devices. ( light socket , switch or receptlales )

The other thing when you sized the circuit with the recessed can we always go by the manufacter max wattage it will listed in the recessed cans reguardless of which type of lamps it being used.

Merci,
Marc
 

· Lic Electrical Inspector
Joined
·
1,844 Posts
You are limited to one 15A general lighting circuit for every 600 sq ft of living space. There is no limit to the number of receptacles on each circuit. If supply lighting outlets, use the maximum wattage allowed for each fixture as a base line and go from there.
 

· Registered
Joined
·
97 Posts
Discussion Starter · #7 ·
You are limited to one 15A general lighting circuit for every 600 sq ft of living space. There is no limit to the number of receptacles on each circuit. If supply lighting outlets, use the maximum wattage allowed for each fixture as a base line and go from there.
So, does this mean that I can only have one lighting circuit for my 325sf kitchen?
 