Hi,
I have a Square D QO120CAFI issue DP-3640 combination AFCI circuit breaker. Basically I bought it to see for myself if these functioned as advertised. It is in a subpanel that supplies the kitchen.
It seemed just fine for about a month, maybe two.
Then it tripped one day. I don't think it was precipitated by an obvious event on the circuit. On the other hand, I think I was in the kitchen (w/the panel) at the time it happened, probably using one or more appliances and perhaps unplugging/plugging something in.
A persistent fault seemed unlikely so I reset the breaker. It popped open right away.
Unplugged all appliances from circuit, still popped.
Shut off breakers to all other kitchen loads. Ditto
I probably disconnected the load side hot wire first. Still popped upon reset.
Then I probably disconnected load side neutral. Still popped.
Tossed the breaker aside for further investigation.
Today I put the breaker back into the panel and tied it to the neutral bar. Still trips, with no load side connections.
It won't trip with the breaker's neutral disconnected, of course.
I've read about the importance of making sure to reset these properly, ie: with gusto. No help.
It seems very unlikely to me that it is "nuisance tripping" in the traditional sense, ie: that the simple fact that there are no load side connections is causing a nuisance trip
It's probably about %80 certain I energized it without any load side connections when I first installed it, it never tripped during or after installation, except on hitting the test button.
So this breaker either suffered infant mortality or was destroyed by a common fault.
How common is this experience?
And, what's the fastest way to get a replacement from Schneider? Assuming things don't work out with the retailer (though I tend to think they will exchange it no questions asked).
-Jeff
I have a Square D QO120CAFI issue DP-3640 combination AFCI circuit breaker. Basically I bought it to see for myself if these functioned as advertised. It is in a subpanel that supplies the kitchen.
It seemed just fine for about a month, maybe two.
Then it tripped one day. I don't think it was precipitated by an obvious event on the circuit. On the other hand, I think I was in the kitchen (w/the panel) at the time it happened, probably using one or more appliances and perhaps unplugging/plugging something in.
A persistent fault seemed unlikely so I reset the breaker. It popped open right away.
Unplugged all appliances from circuit, still popped.
Shut off breakers to all other kitchen loads. Ditto
I probably disconnected the load side hot wire first. Still popped upon reset.
Then I probably disconnected load side neutral. Still popped.
Tossed the breaker aside for further investigation.
Today I put the breaker back into the panel and tied it to the neutral bar. Still trips, with no load side connections.
It won't trip with the breaker's neutral disconnected, of course.
I've read about the importance of making sure to reset these properly, ie: with gusto. No help.
It seems very unlikely to me that it is "nuisance tripping" in the traditional sense, ie: that the simple fact that there are no load side connections is causing a nuisance trip
It's probably about %80 certain I energized it without any load side connections when I first installed it, it never tripped during or after installation, except on hitting the test button.
So this breaker either suffered infant mortality or was destroyed by a common fault.
How common is this experience?
And, what's the fastest way to get a replacement from Schneider? Assuming things don't work out with the retailer (though I tend to think they will exchange it no questions asked).
-Jeff