My husband installed a 18000 btu window unit and it is cutting off and will only run when the test button on the cord it pushed. He did add a double pole 30 breaker and i'm told it's 12 gauge wire. I'm not sure whether to get a new unit or call an electrician! The unit is only a few years old and It does blow cold when it's on.
 

· Registered
Joined
·
1,324 Posts
My husband installed a 18000 btu window unit and it is cutting off and will only run when the test button on the cord it pushed. He did add a double pole 30 breaker and i'm told it's 12 gauge wire. I'm not sure whether to get a new unit or call an electrician! The unit is only a few years old and It does blow cold when it's on.
A test button on the cord?

If it's 12 guage wire, that's too small; you need 10/3 w/ground.

Try and find out from the metal or paper nameplate on the unit what the Current (amperage) requirements are.

Also, if you can, take a pic of the receptacle and the cord and post it here.
 

· licensed electrician
Joined
·
45 Posts
yeah the wire going to the outlet is to small, needs to be 10 AWG but that's not why the pigtail GFCI is tripping, could be a few things, but the one i found most common is a reverse polarity in the receptical, if you have a plug test, make sure the the black and the white aren't reversed any where on the circuit.
 

· Registered
Joined
·
1,324 Posts
The Deez is correct in the cause. I've never seen a pigtail GFCI on a cord, but then I'm not that experienced either. Would these connect similar to a GFCI receptical in that the HOT (Black) wire would be attached to a BRASS clip, while the NEUTRAL (White) would be on a (SILVER)? At the very least, it should indicate which is HOT and which is NEUTRAL. ??
 

· I=E/R
Joined
·
2,052 Posts
The Deez is correct in the cause. I've never seen a pigtail GFCI on a cord, but then I'm not that experienced either. Would these connect similar to a GFCI receptical in that the HOT (Black) wire would be attached to a BRASS clip, while the NEUTRAL (White) would be on a (SILVER)? At the very least, it should indicate which is HOT and which is NEUTRAL. ??
You're getting off base somewhat.
He did add a double pole 30 breaker and i'm told it's 12 gauge wire.
There is no polarity on a 240 volt circuit.
 

· Household Handyman
Joined
·
2,481 Posts
I'm with sparksalot: You will need to know/determine the actual amperage draw on this unit under load then determine if you have the actual correct wire size. The GFCI unit on the cord may be determining a slight high amperage draw on the present 12 gauge wiring and shutting this A/C unit down.
 

· Semi-Pro Electro-Geek
Joined
·
3,404 Posts
Window air conditioners these days have pigtail AFCIs. I think it's rather pointless, but it seems to be a new UL listing requirement or something because they're all doing it. It may be tripping due to an internal problem with the air conditioner. Not sure what external wiring problem could cause the pigtail AFCI to trip. However, as others have mentioned, you need have at least one problem with the circuit: #12 wire cannot be used on a 30A breaker.
 

· Semi-Pro Electro-Geek
Joined
·
3,404 Posts

· I=E/R
Joined
·
2,052 Posts