That doens't explain why the hot is dead or why he's ready 120 on the neutral. If it's being fed from another device it should be lower than 120.
The full voltage is read thru the load on the neutral because without a closed circuit there is no voltage drop.
 

· Jello Wrangler
Joined
·
495 Posts
You don't understand how electricity works. It is not being fed from another device. The voltage is passing through a device on the circuit.
I do, it's symatics "fed" "passing through", whatever. The fact is even if it passes through a device it will have some voltage drop. Both will not read 120v. In fact it's suspect that it's reading 120. Most often it will read between 116v-118v.
 

· Registered
Joined
·
32 Posts
At your breaker do you have 120v to ground? Are your lights on the same circuit breaker and do any of them work? Is anything operational on that circuit? Last thing make sure you don't have a disconnect somewhere that is wired incorrectly (switched nuetral) that you may have overlooked.
Check for an open nuetral. You shouldn't have more than a volt or two max between ground and nuetral. You should really see only a few millivolts. I'd suspect the breaker then the first device that feeds power since none of your outlets work. I would be checking all connections are tight.