Hi, my forced air gas heater recently developed a problem. When I have a filter in, the heat will unpredictably stop heating and blow cold air instead. I read about this being caused by a dirty filter and when I took the filter out and reset it worked fine. However when I put a new filter in I have the same problem. I tried the least resistant filter, MERV 4 or 6, and still had the problem. With the filter now out it hasn't happened in over a month. I'd like opinions on whats wrong before I call a repair guy.
 

· Registered
Joined
·
8,929 Posts
It’s not moving enough air, or the limit has become inaccurate.
It could have been right on the cusp of tripping for a long time and the limit just wore out.
Check airflow and gas pressure. Also check for closed vents, collapsed duct and dirty blower wheel/coils.
 

· Registered
Joined
·
2,617 Posts
Make sure that you are not using too high of an efficient filter. It may make it too hard to pull/push the air through.

And of course, you have changed the filter recentlty, correct?
 

· In Loving Memory
Joined
·
42,671 Posts
If you have A/C the evap coil may be dirty and restricting air flow too much.
 

· In Loving Memory
Joined
·
42,671 Posts
Yes, after the coil gets X dirty, it slows down air flow, and causes the heat exchanger to over heat.
 

· Registered
Joined
·
4 Posts
Discussion Starter · #8 ·
Update:
-Evap coil was clean and shiny, inside and out.
-All vents in the house are open and blowing air. I checked the crawl space for the bottom floor vents and none are collapsed/restricted. Upstairs go through the wall spaces so can't visually check those.
-The blower is clean and seems to be blowing a lot of air. I don't have a way to measure it so that's just a guess really.

One probably important detail I didn't connect to this before - a couple weeks before this happened I had a pretty strong smell of overheated/burnt electrical/electronics. No smoke, just that distinct smell. Never found the source but now thinking it might have been the blower motor seized/overheating.

Repair guy suggested putting the filter back in and checking for error codes the next time it happens, but no obvious cause/solution yet.
 