I have no heat can someone please HELP!

Furnace will not run consistantly,it will glow for start up then go out,some times it will stay lit and most of the time it will go out,it will glow for ignition then go out,and restart.I believe its the ignition control or the integrated furnace control,(had to look that up).its a White Rodgers Model 50A50-405 120v, it says to replace with CNT1309 D340035P01,looked them up unable to find either,the light flashes 3 times at times and stays solid other times,can anyone help?
 

·
Administrator
Joined
·
40,220 Posts
Look on the legend to see what 3 flashes means. Could have a safety that is doing its job.
 
  • Like
Reactions: gettoplumber

·
Registered
Joined
·
2 Posts
Discussion Starter #3
Furnace will not run consistantly,it will glow for start up then go out,some times it will stay lit and most of the time it will go out,it will glow for ignition then go out,and restart.I believe its the ignition control or the integrated furnace control,(had to look that up).its a White Rodgers Model 50A50-405 120v, it says to replace with CNT1309 D340035P01,looked them up unable to find either,the light flashes 3 times at times and stays solid other times,can anyone help?
3 flashes says pressure switch problem,it has been replaced,but still happens,sometimes i get different codes that flash, its not consistant. I'm thinking its a circuit in the control board problem? have looked up the part and White Rodgers says they have no such part,so it must be out dated looked up replacement and couldn't find that either.I have gone down and just moved the wires,it clicks a few times then it will start up and then shut down again,sometimes it will stay on after messin with them and most of the time it won't,haven't seen any bad connections,gas valve is good.
 

·
Administrator
Joined
·
40,220 Posts
Pressure switch code doesn't mean the pressure switch is the problem. It means something is preventing it from closing.
 
  • Like
Reactions: gettoplumber

·
Registered
Joined
·
837 Posts
well....... maybe a few more than three....I however agree many switches that were doing there job have been thrown away..... it usually is something causing it......:eek::eek::eek:
 

·
Registered
Joined
·
4 Posts
exactly just because you get a pressure switch fault doesnt mean that the pressure switch is bad it means that somthing is keeping it from closing. In my opinion your board is probably bad if your getting different codes at different intervals
 