Tenants called me over and said heater was blowing cold air.
Removed cover and saw the pilot flame was lit. The ignition control module is flashing 6+4, which according to the troubleshooting list is "Flame sensed out of sequence - longer than 10 seconds".
From the manual:
Honeywell S8610U 3009
Next system action:
Recommended service action:
Wanted to throw this out here now in case anyone has some advice. The manual says that if the pilot flame is present (which it is), that the gas valve should be replaced. Would this be the correct thing to do, or should i do additional troubleshooting?
Thanks for any help!
Removed cover and saw the pilot flame was lit. The ignition control module is flashing 6+4, which according to the troubleshooting list is "Flame sensed out of sequence - longer than 10 seconds".
From the manual:
Honeywell S8610U 3009
Next system action:
Control waits until flame is no longer sensed and then goes to soft lockout. Flash code continues. Control auto resets from soft lockout after one hour.
Recommended service action:
I turned the unit off, to see if anything changes after an hour. I am about to go over and see if i can clean the flame sensor.Check for pilot flame. Replace gas valve if pilot flame present. If no
pilot flame, cycle "Call for Heat" If error repeats, replace control.
Wanted to throw this out here now in case anyone has some advice. The manual says that if the pilot flame is present (which it is), that the gas valve should be replaced. Would this be the correct thing to do, or should i do additional troubleshooting?
Thanks for any help!