No HEAT! Ch-240 navien how to Purge ??

22526 Views 9 Replies 3 Participants Last post by  zl700
No HEAT! Ch-240 navien how to Purge ?? Where is the fill valve?

Need to know how re add water (purge?) Into my navien heating system.
I thought rhe water feed would do it just by turning valve back on but apprently
There is a different way to add water.

The system was drained to add additional baseboards now cant figure out how to get water back into system

Need to locate the Fill valve on here. Anybody know which night this be in pic?
1 - 10 of 10 Posts
3
Pic

Heres pics ! Might it be the valve in the darker close up image, this valve is marked " aut9 feeder water inlet" and is off

Attachments

See less See more
So there isn't any water pipe connected to the auto water feeder connection on the boiler? Manual designates it as H. I see a back flow preventer piped to it. or at least it looks like its piped to h.
Yes there is a water feed going into "auto feeder water inlet" on bottom.of the boiler. There is a valve on this, this this valve is it. Should I just turn it on for a few to fill up system?
Turn it on. but have a hose connected to that valve that i said in the other thread and purge your system of air.
Seems to keep going, the hose has been running for 10 min now, is this normal?
Did you have the valve below where the hose was connected closed. if so, 10 to 20 minutes is not unusual.
Boiler piping is wrong, check manual

Im surprised you would ever have much heat at all, its piped wrong.
Looks like an attempt at a primary loop off the boiler but the drops between the boiler and the loop are tied together which is wrong.
The boiler flow will never pass by the secondary tees, only heat you get is a bit of gravity/conductive flow. Example on right is best way to get most efficiency and heat transfer requiring you to do some small piping changes.
Also the auto feeder can not feed fast enough to purge your loops above the boiler, proper valving and manual purging is required.

Attachments

See less See more
Easy to do

Easy fix to do before filling, the changes will make it perform 500% better
BTW, the autofeeder on the Navien CH water valve should always be left on, it feeds the correct water pressure electronically.

Attachments

See less See more