No HEAT! Ch-240 navien how to Purge ?? Where is the fill valve?

Need to know how re add water (purge?) Into my navien heating system.
I thought rhe water feed would do it just by turning valve back on but apprently
There is a different way to add water.

The system was drained to add additional baseboards now cant figure out how to get water back into system

Need to locate the Fill valve on here. Anybody know which night this be in pic?
 

·
Administrator
Joined
·
42,390 Posts
So there isn't any water pipe connected to the auto water feeder connection on the boiler? Manual designates it as H. I see a back flow preventer piped to it. or at least it looks like its piped to h.
 

·
Registered
Joined
·
10 Posts
Discussion Starter · #4 ·
Yes there is a water feed going into "auto feeder water inlet" on bottom.of the boiler. There is a valve on this, this this valve is it. Should I just turn it on for a few to fill up system?
 

·
Administrator
Joined
·
42,390 Posts
Turn it on. but have a hose connected to that valve that i said in the other thread and purge your system of air.
 

·
Administrator
Joined
·
42,390 Posts
Did you have the valve below where the hose was connected closed. if so, 10 to 20 minutes is not unusual.
 

·
The Token Engineer
Joined
·
15 Posts
Boiler piping is wrong, check manual

Im surprised you would ever have much heat at all, its piped wrong.
Looks like an attempt at a primary loop off the boiler but the drops between the boiler and the loop are tied together which is wrong.
The boiler flow will never pass by the secondary tees, only heat you get is a bit of gravity/conductive flow. Example on right is best way to get most efficiency and heat transfer requiring you to do some small piping changes.
Also the auto feeder can not feed fast enough to purge your loops above the boiler, proper valving and manual purging is required.
 