The meter can be almost anywhere on the premisis, but you MUST have a service rated disconnect within 30' of the trailer but NOT mounted on or in the trailer.

If I were you I'd read up on Art550 of the NEC.

550.32 Service Equipment.
(A) Mobile Home Service Equipment.
The mobile home service equipment shall be located adjacent to the mobile home and not mounted in or on the mobile home. The service equipment shall be located in sight from and not more than 9.0 m (30 ft) from the exterior wall of the mobile home it serves. The service equipment shall be permitted to be located elsewhere on the premises, provided that a disconnecting means suitable for use as service equipment is located within sight from and not more than 9.0 m (30 ft) from the exterior wall of the mobile home it serves and is rated not less than that required for service equipment per 550.32(C). Grounding at the disconnecting means shall be in accordance with 250.32.
 