Yup he's right...device (outlet) counts as 2 current carrying conductors...not 2 cu inches
1 per receptacle ?
I have only used it as a switch box due to a pocket door
Switch counts as 1 from what I have read ? (
nope I'm wrong - can't even read what I copied & pasted here :laughing
The Chart Says That (NEC Article 314.16.B):
14 Awg. = 2 Cu. In. per conductor,
12 Awg. = 2.25 Cu. In. per conductor
10 Awg. = 2.5 Cu. In. per conductor
8 Awg. = 3 Cu. In. per conductor
6 Awg. = 5 Cu. In. per current carrying conductor counted.
Calculating Current Carrying Conductors
If you are using all conductors of the same size in your box, then you must count the number of current carrying conductors [all colors including white but not counting green or bare] entering your box. Also do not count conductors that neither enters your box nor leaves your box. [pigtails only, these are ignored].
Now add to your number of current carrying conductor list, by counting all of the grounding conductors as one conductor [green or bare], no matter how many grounding conductors, just add the one current carrying conductor to your total number of current carrying conductor list. Remember that all grounding conductors [green or bare] must be counted as a total of one current carrying conductor. NEC Article 314.16.B.5
Clamps are also counted the same as grounding conductors, one current carrying conductor must be added for the total of all clamps found in the box. All clamps found within your box that are entering the box at least ½”, no matter how many, count as a total of one current carrying conductor, only, for all of these clamps. Now add this one conductor count to your total number of current carrying conductor list, if any of these clamps are present. NEC Article 314.16.B.2 A single gang plastic or fiber box will have no clamps to consider. They are exempt from a clamp requirement. NEC Article 314.17.C.Exception
Devices yokes must count as 2 conductors for each device. Count the number of devices {switches or receptacles}. Multiply the total number of devices times 2. The answer from multiplying the total number of devices by the 2 is the total number of current carrying conductors you must add to your total number of current carrying conductor list. NEC Article 314.16.B.4
Now this final total of your current carrying conductor list is the answer to the total number of current carrying conductors installed in your box.