First time posting here- probably not the last as we have just started construction on a garage.



I will be doing the electrical and have a pretty good idea about what to do.

We will be pig tailing from overhead supply (per power company) and attaching new 200 amp meter socket (next to existing meter socket for the house).



From there, I will have SER run about 30' (18" trench/pvc conduit) through footing of garage. I plan on a ufer ground at the sub-panel.
I can't get OH service to garage because of trees or else I'd have a combo on the garage.



I have run a lot of the electrical in the house and everything is good. I keep second guessing myself for the panel/meter and want to be sure I'm doing it correctly. (I have an electrician who has offered to inspect but since I pulled the permit to do the work myself, he can not do the work.)


So, I guess I'm just asking if what I plan on doing makes sense and is to code (I've read about as much as I can of the code).



200A Meter Socket/Main

200A sub-panel

2-2-2-1 Cu in conduit in 18" trench

ufer ground at sub panel

grounding rod at meter-main
 

Attachments

· A "Handy Husband"
Joined
·
15,070 Posts
SER is not rated for underground, conduit or not.

Sent from my Moto E (4) Plus using Tapatalk
 

· A "Handy Husband"
Joined
·
15,070 Posts
Use 4 single conductors rated for wet location.

Sent from my Moto E (4) Plus using Tapatalk
 

· A "Handy Husband"
Joined
·
15,070 Posts
Have you done a load calculation? Why 200 amps to a garage? Will your service support you plan?

Sent from my Moto E (4) Plus using Tapatalk
 

· Registered
Joined
·
5 Posts
Discussion Starter · #7 ·
We will have an apartment above the garage which is why we are going for 200amp. Will have HVAC, stove, water heater, etc. The power company will upgrade with incoming lines from the street to support another 200a - I was planning on a meter socket/main combo that has a disconnect as that is what the house has.
 

· A "Handy Husband"
Joined
·
15,070 Posts
HVAC, stove and water heater for an garage apartment does not need 200 amps. 100 would be plenty, probably 60 would work.

Sent from my Moto E (4) Plus using Tapatalk
 

· Registered
Joined
·
519 Posts
Use THIS Meter Base.

Buy a 320 amp meter base with dual 4/0 lugs. 400amp = 320 amp Continuous.
Both 200 Main Breaker Panels will run directly into the meter base, no need for a disconnect or four wire cable.

Run 4/0 SEU into the house's 200 amp main breaker panel.
If the SEU is more than 3ft long inside the house, you must install a 200 amp Main disconnect and run 4/0 four wire sub feed cable or conduit to the house's 200 amp sub panel.

Run three 4/0 XHHW Aluminun in 3" PVC conduit to the garage.
Use 36" radius sweep elbows and run the conduit directly into the 200 amp main breaker panel in the garage. Use Schedule 80 PVC conduit for the riser at each end to protect against physical damage.

Since this is new construction, you should be able to run the conduit under the garage footer and up the inside wall. This will eliminate the need for Conduit LB's.
Drive Ground Rods and Ground Plumbing at both buildings.

Talk to your inspector about this before you start or purchase material.
Also talk to the Power Company's Engineer and get approval.
I just did this exact setup and it worked very well.

Since this is overhead, run 500MCM XHHW in 3" conduit from the top of the meter to the point of the Power Company's attachment. Again, go over this wire size with your inspector before you start. He/She may permit 350MCM depending on the connected load.
 