Discussion Starter · #1 ·
I'm planning to install 2 new light switches. In the attached picture is it acceptable to run 12/3 from the right junction box to the left junction box to power switch 2? Or do I need to run two distinct 12/2 wires between the junction boxes?
 

Attachments

· Registered
Joined
·
95 Posts
Discussion Starter · #4 ·
Yes that is acceptable.
The only thing I would change is to use the red as the switched conductor between the switches and the black as the constant hot. Personal choice, not required.
Thank you. That makes sense. I will make the change.

Are these 3 way or single pole switches?
Single pole switches.
 