Hello,
I would appreciate input on an idea I have in respect to safety and code. In my garage, I do a little wood working and need a 15amp duplex outlet in the ceiling for a new retractable extension cord.
In the nearby ceiling area I have a single outlet , 30amp 120vdc circuit that powers a dust collector where the startup surge draw is 18 amps. I need a 15amp 120vac outlet in the same area and I want to avoid (if possible) running wires from the load enter.
Do you think it’s safe and within code to pickup the current at the 30amp outlet using the same 10awg wire for a three foot run to a 15amp breaker that would feed a 15amp outlet? I do not see any combination of equipment hooked up or running at the same time where the draw would exceed 30 amps.
Thanks in advance.