1 - 14 of 14 Posts
I am wiring a room with 3 lights and 3 switches. The diagrams I have been using have the neutral wire bypass the switches, so only hit and ground are connected to the switch. I have read both ways of doing this, is hot and ground only the correct way? Thanks!
Background:
12/2 wire on a 15 amp breaker to switch 1.
630954
Switches need always-hot (black) and switched-hot (dotted black, though I prefer red).
Switches do not need neutral at all. Neutral should bypass the switch as per the diagram.
Switches only need ground if the junction box is not metal. If it is, you must attach the ground wire to the metal box no matter what. The switch will pick up ground via its screws and the metal box.
Your diagram does not show a "switch loop". If you are doing a switch loop, then you need to bring neutral to it, so you need /3 cable.
Discussion Starter #3
Thanks. I am not doing a switch loop.. the "switched hot" , can that be the black wire in the romex going from the switch to the light? I currently have it roughed in with a 12/2 wire from the breaker to the switch box, a 12/2 from the switch box to the next switch box and a 3rd 12/2 from the switch box to the light box.
Your diagram is the preferred way of doing it. It keeps the circuit simple and put a neutral in the J-box which is now required by code.....for some time.
But using 14 ga. wire would have made it easier to make the connections.
Discussion Starter #5
Yes..I have realized already the 12/2 was a bit much! The boxes are all plastic, so I'll add a pigtail on the ground to the switch as well as the lights. Thanks
Super Moderator
A switch loop is power to the fixture first and you run 2 wire cable to the switch. Power goes to the switch on the white and comes back switched on the black. It is a loop and there is no neutral.
Discussion Starter #8
So when I run power to the switch first, I can use a 12/2 wire from the switch to the light and that black wire will act as the "switched hot"? Thanks
Licensed electrician
The outgoing black from the switch would be the switched hot.
Reactions: ejs82
So with just the line ana switched hot in the switch bos, how do you install the new tangled smart switches you control with your phone, most of which seem to need a neutral?
A "Handy Husband"
With a 15 amp breaker you only need #14 .
Sent from my moto g power using Tapatalk
The smart switches needing a neutral drove the code change for neutrals in a switch location.
Licenced Electrician
There have been electronic devices requiring a neutral around for decades. The current crop of smart switches, timers and digital dimmers, all relatively inexpensive, gave the code that extra push, yes.
RE: switch loops
631257
The middle diagram no longer meets code but may be grandfathered.
In all cases the wire going to the hot terminal of the light may not be the white one even if marked at the ends with black tape.
<<< So with just the line and a switched hot in the switch box, how do you install the newfangled smart switches you control with your phone, most of which seem to need a neutral? >>>
Don't try this at home. Well ... some folks used the equipment grounding conductor (not shown above) for a neutral.
You would have to string new wiring, for example 12-3 Romex, down to the switch box. Or choose a model of smart switch, timer, etc. which used a battery for internal power.
1 - 14 of 14 Posts