After two days of a burning smell, our furnace failed. The control board was charred, and I picked up a universal board to replace it. ( our very unreliable HVAC guy called Sat morning and allowed to let me pick up the universal board.). The new board didn't have the correct wiring for our older furnace, but all the controls, etc, shown on the new diagram are on the old diagram. Since the univ board calls for separate Hi Limit Output (Hi Lim) and Roll out Switches(RO), and the original circuit had Hi Lim and RO in series, I separated them by making a new loop for RO and reconnected the Hi Lim to the original connector to mate with the 12 pin connector. (To do this I removed wires from the additional harnesses supplied w the kit and added splices to get all the components in their respective places.) I also added a univ. flame sensor to the circuit, positioned it to be in the flame, as well.
After troubleshooting the flashing codes - first polarity, then RO open, I verified connections, removed the RO wires, jumpered them, and, while the flashing light goes to solid, meaning Normal operation, still no joy. It appears everything is wired properly, but, hey, stuff happens, and I must be overlooking something. On my way to pick up two new RO sensors. BTW, the univ board is a White Rodgers 50M56U-843.
After troubleshooting the flashing codes - first polarity, then RO open, I verified connections, removed the RO wires, jumpered them, and, while the flashing light goes to solid, meaning Normal operation, still no joy. It appears everything is wired properly, but, hey, stuff happens, and I must be overlooking something. On my way to pick up two new RO sensors. BTW, the univ board is a White Rodgers 50M56U-843.