Sorry this is so long but I didn't know what info was critical or not to your understanding of what I'm dealing with here.
I've been replacing non-GFCI receptacles in my basement with tamper-resistant GFCI receptacles. So far I've done three. Two had no load to wire up, and one did. I had no issues with any of them and they're all working great.
Now I want to do the one in my garage (pics attached). Unfortunately this one is cabled in a way that the GFCI instructions don't cover, so I need some assistance with that.
The box has two cables, a line and a load. I verified that the line cable is supplying current to the receptacle, and the load cable isn't. I verified that there are receptacles upstairs that the load cable is feeding.
Both the line and the load cables neutral wires are connected as they should be to neutral screws on the receptacle. I verified that neither wire is carrying any current.
The load hot wire (black) is connected as it should be to one hot screw on the receptacle.
Here's what I'm uncertain about in terms of how to wire the GFCI:
The line cable has TWO hot wires (black and red). Both of them are connected TOGETHER to the second hot screw on the receptacle. After disconnecting them both from the receptacle, I verified that both of them are carrying current. Further, with the power off and still disconnected, I checked with a continuity tester and they have continuity with each other. What function are the two hot wires in this cable for?
I'm "just" a DIYer, but I found some issues with the existing wiring that I think need to be corrected, whether I end up installing a GFCI or not:
Assuming I take care of all those issues, then I THINK this is how the GFCI should be wired, but I would appreciate it if people here would verify this:
1. The line cables neutral wire should be connected to the GFCI line "white" terminal (as per GFCI instructions).
2. The line cables black wire should be connected to the GFCI line hot terminal (as per GFCI instructions).
3. The load cables neutral wire should be connected to the GFCI load "white" terminal (as per GFCI instructions).
4. The load cables black wire should be connected to the GFCI load hot terminal (as per GFCI instructions).
5. The line cables red wire should ALSO be connected to the GFCI line hot terminal. There are two back-wire (not back-stabbed) slots, for the same line hot terminal, so one will be for the black and one for the red. THIS IS WHAT I AM MOST UNCERTAIN ABOUT, SINCE A SECOND HOT WIRE FROM THE LINE CABLE ISN'T COVERED IN THE GFCI INSTRUCTIONS.
6. Grounding: Wirenut together these four wires:
I hope this all makes sense! Thank you for your help!
/ Rav
PS: See post #3 from me below for additional info (yes, there's more).
I've been replacing non-GFCI receptacles in my basement with tamper-resistant GFCI receptacles. So far I've done three. Two had no load to wire up, and one did. I had no issues with any of them and they're all working great.
Now I want to do the one in my garage (pics attached). Unfortunately this one is cabled in a way that the GFCI instructions don't cover, so I need some assistance with that.
The box has two cables, a line and a load. I verified that the line cable is supplying current to the receptacle, and the load cable isn't. I verified that there are receptacles upstairs that the load cable is feeding.
Both the line and the load cables neutral wires are connected as they should be to neutral screws on the receptacle. I verified that neither wire is carrying any current.
The load hot wire (black) is connected as it should be to one hot screw on the receptacle.
Here's what I'm uncertain about in terms of how to wire the GFCI:
The line cable has TWO hot wires (black and red). Both of them are connected TOGETHER to the second hot screw on the receptacle. After disconnecting them both from the receptacle, I verified that both of them are carrying current. Further, with the power off and still disconnected, I checked with a continuity tester and they have continuity with each other. What function are the two hot wires in this cable for?
I'm "just" a DIYer, but I found some issues with the existing wiring that I think need to be corrected, whether I end up installing a GFCI or not:
- The box isn't grounded
- The ground of the load cable is just hanging, not connected at all
- The neutral of the load cable is backstabbed instead of being side wired
- There are two wires (line black and red) connected to the same hot terminal, and one of them is barely hanging by a thread on to the screw. They should have been wire nutted together and then pigtailed to the screw.
Assuming I take care of all those issues, then I THINK this is how the GFCI should be wired, but I would appreciate it if people here would verify this:
1. The line cables neutral wire should be connected to the GFCI line "white" terminal (as per GFCI instructions).
2. The line cables black wire should be connected to the GFCI line hot terminal (as per GFCI instructions).
3. The load cables neutral wire should be connected to the GFCI load "white" terminal (as per GFCI instructions).
4. The load cables black wire should be connected to the GFCI load hot terminal (as per GFCI instructions).
5. The line cables red wire should ALSO be connected to the GFCI line hot terminal. There are two back-wire (not back-stabbed) slots, for the same line hot terminal, so one will be for the black and one for the red. THIS IS WHAT I AM MOST UNCERTAIN ABOUT, SINCE A SECOND HOT WIRE FROM THE LINE CABLE ISN'T COVERED IN THE GFCI INSTRUCTIONS.
6. Grounding: Wirenut together these four wires:
- A pigtail from the GFCI ground screw
- A pigtail from the box ground screw
- The ground wire from the line cable
- The ground wire from the load cable (currently not connected at all; it's very short, so I'll have to wire nut on an extension pigtail to that to make it longer)
I hope this all makes sense! Thank you for your help!
/ Rav
PS: See post #3 from me below for additional info (yes, there's more).