OK, that sounds totally doable. I normally use #14 for this sort of thing, but I can make it work with #8 lol.
Harper's Rule:
Buy the wire LAST. (unless you nailed some sweet Craigslist deal.) Don't worry about it, just don't ... do it again.
Honestly, a guy or gal who has the wherewithal to just go out and buy 7500' of #8 copper *on speculation*... that's someone who might put a hot tub, kiln, on-demand water heater, EVSE or 50A RV stand at one of these locations. We will make sure you can do this, since you have the wire.
"But we need to up-size the wire!" Yeah maybe for 200'. Not for this kind of distance. There's a tipping point where you stop throwing cubic metal at it, and pursue other options.
Yeah my problem is, now I'm getting skeptical about your real intent. Nobody puts in a 40A subpanel for a couple outlets and occasional load. I think I'd like to keep some Big Power options in our back pocket. Unfortunately there are choices we'll need to make upfront, since this is conduit not cable. Also I'd like you to fast forward to the Big Power option, so you can see how the conduit and pads need to be placed under those options, so you can plan to be compatible with that for if you ever want to upgrade.
Scenario 1: Cheap-n-Dirty. 120V version.
The problem with this solution is that it requires a white wire in the conduit. The other solutions need a colored wire *instead*. You can't re-mark a white wire to be a hot when it's individual wire in conduit. (unless your AHJ lets you).
Here, we run a Black, White, Green to each outlet location. From there we feed the lights and receptacles. Very straightforward. Since it is one circuit, you do not need grounding rods, which saves a whole lot of rigmarole in the installation. Now let's look at loads.
350' branch: 0.5A normal loads so 0.20% drop using 8 AWG. Add 12.5A of tool load, and you get 5.24% voltage drop.
420' branch: 2.0A normal loads so 0.97% drop using 8 AWG. Add 7A of tool loads, 4.35% drop. Add 12.5A of tool load, and 7.01% drop.
On our 360' extension off that, 1.0A normal loads give 0.41% drop (1.38% total). Add 7A of tool loads, 3.31% voltage drop (totaling 7.66% drop). Add 12.5A of tool loads and 5.59% drop (totaling 12.60% drop).
We're not *supposed* to install more than 8% drop from the main panel. The wire salesmen would certainly prefer we stick to 3% lol. The electrical inspector Will Not Like the 12.60% drop for 12.5A tools, but you could claim your expected load is only 7A and you could just suffer the actual drop. Like I say, we're nowhere near as bad as orange extension cords.
Scenario 2: Cheap-n-dirty: 240V version
Those receptacles are the devil, because it means you need to support any arbitrary 1500W (12.5A) load for that "occasional use". So let's use a 240V/120V stepdown transformer for the rare time when we need 120V tools, That means our 12.5A tool draws 6.25A. That has an amazing effect on voltage drop! Lighting, camera, speaker etc. loads are readily available in 240V.
You wire this scenario exactly like #1. Everything is exactly the same. Except a) you you use NEMA 6-15 outlets (they look almost the same). b) The white wire is now black. And c) choose appliances that have a multi-voltage 120/240V power supply. Which isn't hard these days.
And look what it does to voltage drop!
350' branch: 0.25A normal loads so 0.05% drop using 8 AWG. Add 6.25A of tool load, and you get 1.31% voltage drop.
420' branch: 1.0A normal loads so 0.24% drop using 8 AWG. Add 3.5A of tool loads, 1.09% drop. Add 6.25A of tool load, and 1.75% drop.
On our 360' extension off that, 0.5A normal loads give 0.10% drop (0.34% total). Add 3.5A of tool loads, 0.83% voltage drop (totaling 1.92% drop). Add 6.25A of tool loads and 1.40% drop (totaling 3.15% drop).
Much betta! If you're thinking "wow, all the voltage drops fell by exactly 75%", correct, it falls by (newvoltage/oldvoltage)^2. Ohm's Law x Watt's Law.
Scenario 3: 240V is nice but I want permanent 120V.
"Oh, that'll be easy, just throw the neutral in the pipe and have 120/240V!"
No, that won't work at all. The success of 240V depends on balancing the legs. As you can see, the fixed loads are no problem at any voltage. The problem is that "occasional tool" a single, lump sum 1500W load, that is completely lop-sided. It will load
one hot, and
one neutral,
and the other hot won't help at all. This is exactly the problem with scenario #1!
So forget about it. 4 wires in the pipe doesn't buy you a darn thing.
What will make all the difference in the world is a local 120/240V transformer. That forces every load to be balanced on the 240V supply, in fact, supply neutral isn't even needed or present. In the second scenario we stick a handle on it and make you drag it around, but here we'll permanently wire it. And you might be able to do this without going to a subpanel and all that rot... but Imma do subpanels and all that rot. To accommodate the Big Power scenarios, get a 100A subpanel at least. There's no such thing as too many spaces.
We are going to get a bog-standard supply transformer: 120/240V-240/480V. This transformer has a
- Primary that can be jumpered either for 240V or 480V.
- Secondary that can be jumpered for 120/240V split-phase, or twice as much 120V.
You feed the primary 240V, and jumper the secondary - well, either way you like. I don't care. This then goes to a sub-- hold on, this is actually a
Main Panel, since the transformer makes it a "separately derived service". Ground rods are mandatory here, and you
do install this panel's neutral-ground equipotential bond. It's not a subpanel.
- Size-wise, a typical plug-in tool is 1500 watts, also called 1.5 K VA in the transformer business (VA resembles Watts). So you can use a "1.5 KVA transformer" - but if you do, make sure to jumper it for 120V or it will overload. The 1.5 KVA transformer will give you voltage drops similar to scenario 2.
- If you want 5000 watts at that location, a common size seen for $100 on Craigslist is a "5 KVA transformer", giving 20A @ 240V or 2 legs of 20A @ 120V. Your voltage drop will depend on actual load, but it'll be in proportion to scenario 2. 5 KVA is probably as big as you want to go before voltage drop starts beating you up.
Scenario 4, 480V: Now you're playing with power
The trick with 480V is you have to lay out the conduits and transformer pads so the 480V is entirely contained within the transformer casings, there is no way to access the conduit anywhere else, and there is nothing serviceable inside the transformers. Very few "Danger: 480V" covers, and no reason whatsoever for a homeowner to pop one off. By the way, 480V isn't that scary; Britain brings 416V into people's homes and right into their panels.
Now you have a transformer sitting at the home, being fed by 100A of 240V. That backfeeds the secondary of the transformer. The primary is jumpered for 480V and attached to our long wires. At each location, the conduit pops up *inside* the transformer cowling, and is jumpered straight to the transformer primary. The overcurrent protection is the 100A breaker in the main panel.
Other than that, it's like Scenario 3, with sub---darn it -
main panels everywhere.
Calcwise, as you may gather, it falls by (480/120)^2 so all our example voltage drops are now sub-1%. Not even worth calculating. Let's try something big.
A 50A RV stand at the far (780') location that's maxed out at 50A full draw - cooking+dryer+A/C whatever. That is 12,000 watts, or
[email protected] Voltage drop calculator says, for
[email protected] on #8 wire -- 5.61% drop. Meh, but that's with the RV running at total redline. Normally voltage drop will be lower.
Scenario 5, 600V: Max #8
Mind you, we're starting to spend some serious money on transformers here.
Same thing as above but we are using 120-240/600V transformers. Our nameplate wire capacity is 30,000 watts. Now you're at a 125A breaker trip with 30 KVA transformers. Same as above.
Your RV load at the far end, pulling full 50A about to trip its own breaker, is 3.59% drop.
If you had a 100A on-demand hot water heater at the intermediate location (420'), your voltage drop would be 3.87%.