What follows is an educational point! I'm not sniping at anyone. There is one thing about your installation that I want to point out. The US National Electric Code forbids using a raised cover as an Equipment Grounding Conductor (EGC) Unless it meets the specific requirements in 250.146,
as yours does. If it doesn't comply with these very specific requirements the receptacle grounding terminal must be connected to the EGC by a wire or other approved method.
"250.146 Connecting Receptacle Grounding Terminal to Box.
An equipment bonding jumper shall be used to connect the grounding terminal of a grounding-type receptacle to a grounded box unless grounded as in 250.146(A) through (D). The equipment bonding jumper shall be sized in accordance with Table 250.122 based on the rating of the overcurrent device protecting the circuit conductors.
(A) Surface-Mounted Box. Where the box is mounted on the surface, direct metal-to-metal contact between the device yoke and the box or a contact yoke or device that complies with 250.146(B) shall be permitted to ground the receptacle to the box. At least one of the insulating washers shall be removed from receptacles that do not have a contact yoke or device that complies with 250.146(B) to ensure direct metal-to-metal contact.
This provision shall not apply to cover-mounted receptacles unless the box and cover combination are listed as providing satisfactory ground continuity between the box and the receptacle. A listed exposed work cover shall be permitted to be the grounding and bonding means when
(1) the device is attached to the cover with at least two fasteners that are permanent (such as a rivet) or have a thread locking or screw or nut locking means and
(The way I read (A)(1) is that locking washers would be enough to satisfy this.)
(2) when the cover mounting holes are located on a flat non-raised portion of the cover."
Like this one
View attachment 674525
Not like this one.
View attachment 674524
The reason for the restriction is that common boxes and covers are made of mild steel and, even though they are galvanized, the connection between them will corrode open if the installation is not carefully done and both box and cover lend themselves to a lot of metal to metal contact area. The connection corroding open did not seem to happen if the cover had the more recently available recessed corners were the screw holes are because that avoided the box getting distorted out of contact with the open edge of the box. If the box and cover make continuous contact all the way around the connection between them holds up well.
What can I say. I have a need to stay curious and try to discover new things about what I'm doing. Before I would open a raised cover to work in that box, while I had my Vol-Con Audible out already to check that I had turned off the correct breaker, I often checked the continuity between a mounting screw of the cover and the receptacle cover screw. The older hands will remember that the receptacles were held to the back of the raised cover by its single threaded cover screw hole. If the connection was dubious by sight or continuity check I would improve it. If it was loose from it's cover I would conclude that the way it was being used tended to loosen it. I'd drill the 2 holes through the ones on the screw yoke and throw in 2 extra 6/32 screws and nuts. I wasn't more knowledgeable than many of the people I worked with. I just would get bored it I didn't keep actually looking at and thinking about the work more than just enough to install it. I think that is why I moved into fire alarm system and control work and also why I when on into remote, alternative power sourced, communications shelter installs all over this hemisphere of the globe.
You are going to support that EMT within 3 feet of every box aren't you?" That means any length more than 6 feet gets 2 clamps or straps.
Tom Horne