Does anyone happen to know the NEC section that covers isolating neutrals from grounds in subpanels?

Having a discussion with someone and I can't find it. Thanks!
 

·
UAW SKILLED TRADES
Joined
·
5,341 Posts
250.32 (b)(1)for buildings or structures detached from the structure or building with the service equipment.

250.24(a)(5) for load side of service equipment.

Note prior to 1996 code cycle you were allowed to bond a 3 wire feeder to a detached structure or building. There are many thousands of those existing today, especially in farm and rural settings. Not to mention the 3 wire dryer and ranges out there.
 

·
Licensed electrician
Joined
·
13,387 Posts
Do you mean in the same building as the service?
 

·
Licensed electrician
Joined
·
13,387 Posts
They have always required a 4 wire feeder and isolated neutrals and grounds as long as I know.

The exception was to a detached structure as was already mentioned. This was allowed only if there were no metallic paths between the structures like a water line, phone or cable etc.
 

·
Licensed Electrician
Joined
·
4,352 Posts
250.24 (a)(5)

load-side grounding connections. A grounded conductor
shall not be connected to normally non–currentcarrying
metal parts of equipment, to equipment grounding
conductor(s), or be reconnected to ground on the load side
of the service disconnecting means except as otherwise permitted
in this article.
 