Hi all. I am running a new pole barn 200 Amp service. According to NEC 2008 what size aluminum wire do I need to the meter and to the barn. The weather head is about 20" above meter and it is 30 feet underground to the barn. Thanks, Rob.
 

· Registered
Joined
·
11,194 Posts
I would get on the phone and call around.
Home Depot doesn't carry it to my knowledge. I would try electrical supply houses.
Since you are looking for shorter lengths, some outfits may have to order it from their cutting location.

You ask for 250kcmil aluminum.
 

· Rob
Joined
·
1,036 Posts
Discussion Starter · #9 ·
I would get on the phone and call around.
Home Depot doesn't carry it to my knowledge. I would try electrical supply houses.
Since you are looking for shorter lengths, some outfits may have to order it from their cutting location.

You ask for 250kcmil aluminum.
Thanks. I am not going to have a lot of power in the building. I wonder if the inspector will let me get away with 4 AWG. If I would have known I would have gone 100 Amp. It is not easy getting supplies around here.
 

· Rob
Joined
·
1,036 Posts
Discussion Starter · #11 ·
Go to the local Electrical warehouse. They will be better and also will make sure that you have everything that you need.

The big box stores, you end up wasting more time waiting on someone to help you.
Thanks, I just called the only one around and they said they would have to order it. I am waiting for the inspector to get back to me to see if I can use 4 Awg.
 

· Banned
Joined
·
17,162 Posts
Most places are like that, because they are ordering enough for just the customer's job.

The spool would end up being bigger then they could handle, if they actually had to keep it on hand.

If the min. is say 6, you can go larger if you want to say 2. I imagine if you order before 4, they may get it in on Monday. Otherwise you are probably loking at Wed.
 

· Rob
Joined
·
1,036 Posts
Discussion Starter · #14 ·
Most places are like that, because they are ordering enough for just the customer's job.

The spool would end up being bigger then they could handle, if they actually had to keep it on hand.

If the min. is say 6, you can go larger if you want to say 2. I imagine if you order before 4, they may get it in on Monday. Otherwise you are probably loking at Wed.
I am still hoping the inspector will say 4 awg. He might not even know. We are pretty rural out here.
 

· Lic Electrical Inspector
Joined
·
1,844 Posts
4/0 AL is rated for 185A. Unless your calculated load exceeds 185A, that is all you need. Save your money.
 
  • Like
Reactions: gregzoll

· Lic Electrical Inspector
Joined
·
1,844 Posts
Robpo said:
I am still hoping the inspector will say 4 awg. He might not even know. We are pretty rural out here.
The inspector may tell you whatever meets code.
 
  • Like
Reactions: gregzoll

· Registered
Joined
·
11,194 Posts
I am waiting for the inspector to get back to me to see if I can use 4 Awg.
Not if you are running a 200 amp service to the pole building.
If you are running power to the pole building from a service panel at the meter location, you can install a smaller breaker in that panel, and limit the service/wire size to the pole building.

If for example you used a 60 amp feeder breaker, your wire would be sized on the 60 amps, even if you installed a 100 or 150 amp panel in the pole building. It's still a 60 amp service to the building. Get a main breaker type panel for the pole building, you need a main disconnect there.

BTW, is your weather head really 20 inches above the meter ? I assume you meant 20 feet.
 

· Rob
Joined
·
1,036 Posts
Discussion Starter · #20 · (Edited)
Not if you are running a 200 amp service to the pole building.
If you are running power to the pole building from a service panel at the meter location, you can install a smaller breaker in that panel, and limit the service/wire size to the pole building.

If for example you used a 60 amp feeder breaker, your wire would be sized on the 60 amps, even if you installed a 100 or 150 amp panel in the pole building. It's still a 60 amp service to the building. Get a main breaker type panel for the pole building, you need a main disconnect there.

BTW, is your weather head really 20 inches above the meter ? I assume you meant 20 feet.
Yeah I got a little mixed up under stress. I feel better now.
That is a good idea I didn"t think of that. I may do that sometime down the line. Can I just get a new main breaker. The panel is installed.
 