I recently did a complete overhaul of my natural gas distribution system. This is always a subject that generates discussion – should a DIYer try it or not? My conclusion is that if you are willing to do quite a bit of advance research (including reading up on code requirements), put an equal amount of time and energy into making a flow and pressure diagram (which involves many hours of consultation of flow and pressure tables), and then do the work slowly, carefully, and with LOTS OF LEAK TESTING, it is absolutely within the power of a reasonably handy DIYer.
But that aside, since I completed the project I’ve had two mysteries with my maxitrol line regulator. Any Sherlocks out there?
Mystery One: At one point the gas was off at the meter and the system was full of air. When the gas was turned back on at the meter, the gas was absolutely entering the regulator at 2psi (55 inches wc, I have a gauge) but the pressure coming out was ZERO – nothing coming out of the regulator at all (I have another gauge downstream of the regulator). To try something, I bled the line to the hot water heater – and that worked! The pressure coming out of the regulator went from zero to 9” wc and stayed there, just where it’s supposed to be.
Don’t get me wrong, I’m happy to take “yes” for an answer. But I’m very curious: Why on Earth would the regulator have not been putting out anything at all, and why would bleeding the line to the hot water heater solve the problem?
Mystery Two: After the water heater, I bled the line to the furnace. I ran into a little trouble there – after I tightened everything up, the leak solution showed evidence of a very tiny leak where the tube entered the fitting that goes into the valve at the furnace. It was a very, very small leak, but there is no such thing as an acceptable leak, so I took it apart and redid the connection…but that didn’t stop the leak. So I grabbed my wrenches and tightened the nut for everything I was worth, and succeeded in moving it about 1mm around. But that was enough! The leak solution showed no leak. Good as gold.
But the mysterious thing was, after I got the nut as tight as I could and stopped the leak, the pressure coming out of the regulator moved from an even 9 inches wc to 9.8 inches wc.
This leak was about as small as you could get -- just the smallest bubbles imaginable that formed slowly and few in number. Why would stopping a very, very tiny leak result in almost a full inch of change in pressure?
For the record, since these events, the pressures have been as steady as can be. 55 inches wc coming in, and 9.8 inches wc coming out.
Any ideas out there? And does anyone think the regulator might be damaged or defective?
But that aside, since I completed the project I’ve had two mysteries with my maxitrol line regulator. Any Sherlocks out there?
Mystery One: At one point the gas was off at the meter and the system was full of air. When the gas was turned back on at the meter, the gas was absolutely entering the regulator at 2psi (55 inches wc, I have a gauge) but the pressure coming out was ZERO – nothing coming out of the regulator at all (I have another gauge downstream of the regulator). To try something, I bled the line to the hot water heater – and that worked! The pressure coming out of the regulator went from zero to 9” wc and stayed there, just where it’s supposed to be.
Don’t get me wrong, I’m happy to take “yes” for an answer. But I’m very curious: Why on Earth would the regulator have not been putting out anything at all, and why would bleeding the line to the hot water heater solve the problem?
Mystery Two: After the water heater, I bled the line to the furnace. I ran into a little trouble there – after I tightened everything up, the leak solution showed evidence of a very tiny leak where the tube entered the fitting that goes into the valve at the furnace. It was a very, very small leak, but there is no such thing as an acceptable leak, so I took it apart and redid the connection…but that didn’t stop the leak. So I grabbed my wrenches and tightened the nut for everything I was worth, and succeeded in moving it about 1mm around. But that was enough! The leak solution showed no leak. Good as gold.
But the mysterious thing was, after I got the nut as tight as I could and stopped the leak, the pressure coming out of the regulator moved from an even 9 inches wc to 9.8 inches wc.
This leak was about as small as you could get -- just the smallest bubbles imaginable that formed slowly and few in number. Why would stopping a very, very tiny leak result in almost a full inch of change in pressure?
For the record, since these events, the pressures have been as steady as can be. 55 inches wc coming in, and 9.8 inches wc coming out.
Any ideas out there? And does anyone think the regulator might be damaged or defective?