#6wire from panel to airhandler with 60 amp breaker if running 15 kw heat strips,# 10/3 wire from panel with 30 amp breaker at panel running to a/c condensor with pullout non fuse box, or 30 amp breaker box also you will need a/c whip from there to your unit, as for other wire your running it depends on what amps are required for the system, 20 amps requires #12 wire