Okay Let me see if I got this right. I would like to run (2) 20 amp circuits in (1)1/2" EMT for an approximate length of 70 feet with receptacle every 5 feet so each receptacle as on a different circuit then the one next to it. If I understand it right I can share the neutral and the breakers would have to be on separate legs of the bus?

Am I still good with 12ga.wire? Not planning on running anything to terrible heavy on it. Planning on running 1 white,1black,1red wire.

Thanks
Gary
 

· Electrical Contractor
Joined
·
1,054 Posts
Too many times I've had my d**k knocked in my watch pocket from disconnecting neutrals from a multi-wire circuit.
Especially from 3-phase 480, where the neutrals were being shared on 3-277 volt lighting circuits.
Not a good feeling when you're on a 10-12' step ladder or sitting on top of walk-in cooler/freezer and you only have 2' between the top of it and the steel joist.:no:

If you were to come behind me on any of my jobs, no worries, I do not share neutrals.:thumbsup:
 

· Banned
Joined
·
2,487 Posts
Too many times I've had my d**k knocked in my watch pocket from disconnecting neutrals from a multi-wire circuit.
Especially from 3-phase 480, where the neutrals were being shared on 3-277 volt lighting circuits.
Not a good feeling when you're on a 10-12' step ladder or sitting on top of walk-in cooler/freezer and you only have 2' between the top of it and the steel joist.:no:

If you were to come behind me on any of my jobs, no worries, I do not share neutrals.:thumbsup:
I personally don't favor the double pole MWBC requirement, but I have to ask, why are you taking so many shared neutrals apart? And are you not concerned about putting 480 across 277 V loads? It only took me one time to learn about the snake hidden inside the shared neutral...
 

· Electrical Contractor
Joined
·
1,054 Posts
This was many years ago. Just think it's a good idea.

Also, we were doing a Sears remodel and work was being done during store hours and cutting lights off in the store wasn't an option. Just situations like this required some wires to be disconnected.
 

· Electrical Contractor
Joined
·
1,054 Posts
Not everyone does things the way they're supposed to. I've just run into a lot of crap in my days. Some plants I've worked in, over the years a lot of jack leg crap was done.
When you open a box and pull the wires out and the wire nut practically falls off and the stranded wires pull apart cause there's 10 of them in a 76 wire nut and you need the one in the middle. People tapping in wherever they can. 100-200 panels where this circuit may be over here and this one may be over there, nothings labeled or labeled incorrectly.

I've even seen 120 volt circuits and the neutral from the 277 being used.

It's all good when you're just doing new construction and everything's laid out for you. Just run pipe, pull wires and terminate. When you have 1 million+ square foot facilities that have been around for 20 or 30 years, there's no telling what you'll run into.

If you think you can just turn off what you want when you want, it just doesn't happen that way.
 

· Union Electrician
Joined
·
615 Posts
Also, we were doing a Sears remodel and work was being done during store hours and cutting lights off in the store wasn't an option. Just situations like this required some wires to be disconnected.
I understand what you're saying. Neutrals under load can pack a whallup. But if you can't shut them off anyway, what use is a multi-pole breaker in this situation?
 