I have 400 amp service to my house. At the meter base, this is divided into 2 200amp subpanels. One is for the detached shop, and the other for the house (passing thru a Generac whole-house transfer switch.
What I would like to do, and I believe to be permitted under NEC 225.30(A)(3), is to, in addition to the 125 amp service to the shop, run a 15 amp circuit, 12-2 UF-B to the shop, that comes off of that panel serviced by the backup generator. This would come under the exception of "optional standby systems".
This would be to supply power to a single outlet supplying the alarm system controller and video camera system, that would be backed up by the automatic generator.
If I read it right, all that is required is a disconnect of the secondary feed, and proper labeling and documentation of such.
What I would like to do, and I believe to be permitted under NEC 225.30(A)(3), is to, in addition to the 125 amp service to the shop, run a 15 amp circuit, 12-2 UF-B to the shop, that comes off of that panel serviced by the backup generator. This would come under the exception of "optional standby systems".
This would be to supply power to a single outlet supplying the alarm system controller and video camera system, that would be backed up by the automatic generator.
If I read it right, all that is required is a disconnect of the secondary feed, and proper labeling and documentation of such.
Right or wrong??Number of supplies
If more than one building or other structure is on the same property, each building/structure must be served by no more than one feeder or single or multiwire branch circuit [225.30]. However, there are five exceptions to this. You can have additional supplies for:
1. Special conditions [225.30(A)]. These are:
• Fire pumps.
• Emergency systems.
• Legally required standby systems.
• Optional standby systems.
• Parallel power production systems.
• Systems designed for connection to multiple sources of supply for the purpose of enhanced reliability.
2. Special occupancies. Multiple-occupancy buildings where there’s no available space for supply equipment accessible to all occupants, or a building/structure so large that two or more supplies are necessary — but only with special permission [225.30(B)].
3. Capacity requirements. Where the capacity requirements exceed 2,000A [225.30(C)].
4. Different characteristics. Different voltages, frequencies, or uses, such as control of outside lighting from multiple locations [225.30(D)].
5. Documented switching procedures. Additional supplies are permitted where documented safe switching procedures are established and maintained for disconnection [225.30(E)].