Discussion Starter · #1 · (Edited)
Ok, I've edited this post (eliminated all but one of the questions), because I discovered a really good youtube video by Goodman, or about Goodman - or maybe it was just a Goodman ad in the opening of the video? Anyway, it answered my previously posted questions here, except for the remaining one below. The video:

http://www.youtube.com/watch?v=JE3MzApSN7E Title of the video:Grounding & Flame Rectification.wmv, by instructor12b


The following paragraph (in italic) is excerpted from Fieldpiece's Tech Articles, located at

http://fieldpiece.com/tech-articles/138-service-tips-examining-flame-rectification (the excerpt is found toward the bottom of the page, below the drawings that illustrate how to hookup the fieldpiece multimeter.

"Make sure there is AC voltage between the flame diode and the base of the flame. Measure AC voltage from the flame sensing rod to the base of the flame. The value varies by model (in neighborhood of 90V), but the important thing is to ensure that there is voltage present."

How do you accomplish this test since the end of the flame sensing rod and the end of the burner tube are inside the heat exchanger ?.....

Thanks much for any help.
 

· Registered
Joined
·
1,407 Posts
Just put the meter in series with flame sensor. The meter needs to be in micro amps . You soils get around 2-4 micro amps not less than 2

Sent from my iPhone using DIY Forum
 

· Registered
Joined
·
1,436 Posts
Discussion Starter · #3 ·
JJBoy, thx for your reply. I found a great video on youtube that answered all but one of my questions, so I edited my post except for one remaining question. I know how to hook up and do the uA's test, but would like to know how to check this voltage also, if you can help... Please see original post.
 

· Registered
Joined
·
1,436 Posts
Discussion Starter · #8 · (Edited)
I separated the quick disconnects on the flame sensor lead, inserted meter probes and on the first try, the uA's-dc was all over the place... all under 1.0 uA. On the next try, it was still all over the place, but as high as 1.9 this time.

Voltage on the first and only try/measurement was 104 vac, measured on the lead coming from the control board, to cabinet (after I separated the quick disconnects).

This ignition failure (a repeating one flash & pause... from the board's green led light) happened at the same time as the igniter failure. The igniter had a small crack and hot spot (minimal hot spot, of course) around the crack. Possible that this igniter failure fried the control board (arcing at the crack?), since this ignition failure condition (flame going out soon after coming on) surfaced immediately after the igniter failure?

I installed new igniter and flame came on first time, but went out 5 seconds later, and continues to do so. There is no delay between flame going out and any click of the gas valve, or relay on the board - it's simultaneous. If there's any click from a relay on the board (when flame goes out), it's drowned out by a larger click/noise coming from the gas valve, I believe ( the "flame going off" click sounds more like the louder click/noise of the gas valve when it first lights up).

I took this flame sensor to a former tech at the supply house counter, and he said there was no need to install a new one. He ohms checked it end-to-end (very close to zero ohms), and from sensor rod to its mounting bracket (no shorting thru the insulator). . Insulator was not cracked or discolored. The rod itself was pretty clean before and after I scrubbed it up with steel wool. Still no help.

I'm confident that this flame is full (have seen a couple of weak flames before) and sufficiently enveloping the flame sensor.

The end of burner tube and its projecting tab are both clean and in very good condition.

Combustion air motor remained working as good as it was on startup sequence.

Is it possible this flame sensor still could be bad, despite its good appearance and ohms testing (and no shorting to mounting bracket)?

Ground connection from control board multi-pin connector to cabinet is good - took it off scrubbed it a bit to be sure.

If I haven't mentioned it yet, this is a mobile home furnace (ignore the "A" and "B" labeling in the pic):

 

· Registered
Joined
·
1,436 Posts
Discussion Starter · #10 · (Edited)
Beenthere, have never done that yet - don't have a water column guage, if that's the correct guage.

You're thinking lack of pressure is possibly shutting down the gas valve, distorting the flame, or is responsible for the fluctuating uA's test, or something of that nature?

Thx for jumping in here...
 

· In Loving Memory
Joined
·
42,671 Posts
They may or may not check the manifold pressue. they may only check the pressure that their meter/reg is supplying.
 

· Registered
Joined
·
1,436 Posts
Discussion Starter · #14 · (Edited)
Ok - Not sure if he would have checked it or not (I wasn't there), but he said there was no place to hook up on the gas valve - whatever that means.

If it's of any help at all, this gas valve is not as big (not as bulky or box-y lookin') than other gas valves I've seen on older furnaces in an older mobile home park. Both, the ones on the standing pilot-type furnaces and the ones on the electronic ignition-type furnaces, are bigger and boxier looking than this one. Looking directly at this one, while kneeling in front of the furnace (gas valve installed), it does have a bit of a boxy "profile" (looking at it straight on), but is considerably shallow in depth (horizontal depth, front to back as I look at it while kneeled in front of it) by comparison (to the others just mentioned).

The only other thing he said was that there was no problem with the gas line pressure feeding the gas stove normally (just eye-balling its performance).

After minimal google-ing, manifold pressure is taken near the outlet of the gas valve? Anyway, homeowner says she's going to have to wait a bit before calling out an hvac pro, and said in the mean time if I could come up with anything else, she would welcome me back for additional fix-it attempts.

I do know what you mean, though, about Duke maybe checking pressure (in the house), but maybe not. Occasionally, I call them out for an electrical problem - some will come in the house and go above & beyond... some won't.

Thx much for your help.
 

· Registered
Joined
·
1,436 Posts
Discussion Starter · #15 · (Edited)
I was talking to a supply house today and the rep checked this furnace model number against an ongoing recall list (Coleman). This furnace is on the list... for a possible overheat condition, strong enough to reach the drywall of the furnace closet. No injuries reported yet, but several property damage claims so far.

I then went to the recall website (address posted below), discovered they're providing free inspections and a preventative correction-type fix for the problem, via local contractors. Don't know all the details, but one of the fix's mentioned was installation of a shield to contain any overheating. Another one of the fix's, obviously, is a new heat exchanger if warranted.

I explained about the control board's flashing green light/diagnosis of ignition failure - contractor said he could take care of the recall fix as well as the ignition failure, without charge to the homeowner. Contractor is coming out tomorrow for inspection and confirmation of the the model number. Probably return the following day for the recall fix and repair, he said. I'll post here again when contractor is finished.

Model numbers of affected furnaces:

The Coleman®, Coleman® Evcon, and Red T furnaces are used in manufactured housing. On these furnaces the name plate is found mounted on the left inside surface behind the lower panel. The furnaces are a silver color with white access panels.

  • DGAT070BDD
  • DGAT070BDE
  • DGAT070BDF
  • DGAT075BDD
  • DGAT075BDE
  • DGAT075BDF
  • DGAM075BDD
  • DGAM075BDE
  • DGAM075BDF
  • DLAS075BDD
  • DLAS075BDE
  • DLAS075BDF

These model numbers, and additional information, are found at this website address: http://www.dgatprogram.com

The Recall Program Support Center at (888) 665-4640.
 

· Registered
Joined
·
1,436 Posts
Discussion Starter · #16 ·
I was talking to a supply house today and the rep checked this furnace model number against an ongoing recall list (Coleman). This furnace is on the list... for a possible overheat condition, strong enough to reach the drywall of the furnace closet. No injuries reported yet, but several property damage claims so far.

I then went to the recall website (address posted below), discovered they're providing free inspections and a preventative correction-type fix for the problem, via local contractors. Don't know all the details, but one of the fix's mentioned was installation of a shield to contain any overheating. Another one of the fix's, obviously, is a new heat exchanger if warranted.

I explained about the control board's flashing green light/diagnosis of ignition failure, and contractor said he could take care of the recall fix as well as the ignition failure, without charge to the homeowner. Talked with the contractor today, and someone's coming out tomorrow for inspection. Probably return the following day for the recall fix and repair, contractor said. I'll post here again when contractor is finished.

Model numbers of affected furnaces:

The Coleman®, Coleman® Evcon, and Red T furnaces are used in manufactured housing. On these furnaces the name plate is found mounted on the left inside surface behind the lower panel. The furnaces are a silver color with white access panels.

  • DGAT070BDD
  • DGAT070BDE
  • DGAT070BDF
  • DGAT075BDD
  • DGAT075BDE
  • DGAT075BDF
  • DGAM075BDD
  • DGAM075BDE
  • DGAM075BDF
  • DLAS075BDD
  • DLAS075BDE
  • DLAS075BDF

These model numbers, and additional information, are found at this website address: http://www.dgatprogram.com

The Recall Program Support Center: (888) 665-4640.
 

· Registered
Joined
·
1,436 Posts
Discussion Starter · #17 ·
My apologies for not getting back sooner. I thought I had. This is what happened:

Contractor came out to handle the Recall service.

This pic is not the actual furnace, but is a match.



First thing he did was to attempt starting the furnace. After he watched it shut down a few times, he checked manifold pressure - was 3.6 (spec on the gas valve was 3.5, natural gas). He checked flame sensor and agreed it was good. After finding no other obvious problems, he went ahead with the heat ex-changer replacement and said he would check the shutting down problem some more after finishing the recall work.

I watched the entire removal/replacement process, and there was no blockage around the baffle in the upper part of the heat ex-changer, nor in the stack above it going to the roof jack. After completing the replacement, he turns the furnace on and it was like it never had a problem to begin with!

When this contractor was attempting to start the furnace, before beginning the recall work, it was acting differently than it had been with my attempts, which were flame on, then shut down 5 seconds later. When he did it, the flame was coming on, but so was the blower, almost immediately. The flame would shut off in about 5 seconds, but the blower would keep on running. It was different with him, because he had the Fresh Air switch On, and my attempts were with that switch turned Off. During my initial attempts on my first day out there, I also tried it with the Fresh Air switch On, and got the same results as the contractor did, but all my subsequent attempts were with that switch turned Off.

For other non-pro's like myself, this furnace is a Coleman Evcon, Standard Blend Air II (there is also a more complex Deluxe Blend Air II furnace). Contractor was not familiar with it - I did some google-ing. This Standard model furnace has only a roof vent with a flex duct leading down to the furnace closet where it terminates at the upper left corner of the closet compartment, with an adjustable damper at its end, controlled by a motor (the Deluxe model has an attic fan and a couple of control boards, plus more switches in the furnace closet).

So, for this Standard model in question now... when the blower is on, this damper is opened to introduce fresh air into the home. The front panels of the furnace are vented (with filters) and the blower draws the fresh air into the cabinet and over the heat ex-changer and out to the floor vents (this is a mobile home). I've described this system, in case it's possible that this Fresh Air component could have anything to do with the flame shutting off prematurely. In retrospect, maybe I should have temporarily disconnected this Fresh Air component from the thermostat, or wherever it's connected to, to see if it was the problem.

The front of this furnace was very dusty, including the top surface of the control board, which was mounted horizontally in the box (labeled "A" in the picture). Neither the contractor nor I, ever did clean it (he didn't get a chance to - furnace starting working after his recall work). All I did was to remove and re-attach the two multi-pin connectors on the board in case they were not making good contact. I had also removed and re-connected connections at the Combustion Air motor, and switch or whatever that thing below the motor is called. Maybe that component proves induction air after achieving certain RPM speed of the motor (read about that somewhere)? I had also separated and reconnected the connector on top of the rectangular box ("A", in the pic).

If all the dust wasn't a factor, maybe the flame sensor circuit had a better ground after all the dis-assembly and re-assembly of the furnace walls, during the heat ex-changer replacement?
 